I suspected you had a Giandel.
Can you please do a couple of tests and report back.
With the Giandel powered off please check for continuity between these points and report back.
equipment ground and ac ground
equipment ground and ac neutral
equipment ground and ac hot
ac ground and ac neutral
ac ground and ac hot
 
Do I need the DC cables connected first with DC power applied or can I just do it out of the box.
 
Last edited:
Do I need the DC cables connected first with DC power applied or can I just do it out of the box.
Out of the box should be fine.
Thanks.
Two more tests if you please.
dc negative to equipment ground
dc positive to equipment ground
 
Just got to work, brought it with me to do the testing. Get back to you soon with the results.
 
equipment ground and ac ground .5 ohm
equipment ground and ac neutral. Open
equipment ground and ac hot. Open
ac ground and ac neutral. Open
ac ground and ac hot. Open
dc negative to equipment ground. Open
dc positive to equipment ground. Open
 
equipment ground and ac ground .5 ohm
Surprised the resistance is that high.
equipment ground and ac neutral. Open
Floating neutral.
It is what it is.
equipment ground and ac hot. Open
expected
ac ground and ac neutral. Open
Floating neutral
ac ground and ac hot. Open
expected
dc negative to equipment ground. Open
I guess that is correct.
If it were bonded then you could run the inverter with the dc negative disconnected

dc positive to equipment ground. Open

@FilterGuy please check my reasoning.
 
Surprised the resistance is that high.

<0.5 ohm>

Typical contact resistance. Sometimes you can zero or subtract that if fairly repeatable.
Not everybody has a 4-wire meter.
It would take quite a bit of wire to actually have half an ohm.
 