kenkoh
Solar Enthusiast
Gone through Will's book again and the guides are mainly for 12v systems. Thanks.
24v fuseing is the same as 12v just that your amperage is half what 12v would be for the same wattage. If you are calculating amps the fuses are the same as they would be for 12v at the same amperage.Gone through Will's book again and the guides are mainly for 12v systems. Thanks.
It's based on amperage. 1500W / 12V / 85% = 150A. 1500W / 24V / 85% = 75A. It's those different amperages that give you the different wire size.But the wire size are different for the same length, say for a 1500w inverter to battery the wire is 1 awg for 12v but 4 awg for 24v. Is there a wire size chart specifically for that?
Yes he's reputable.I see. Thank you again. I just found this calculator today, can I trust it? https://www.explorist.life/wire-sizing-calculator/
Would I use a 80a fuse for the 24v 1500w inverter?It's based on amperage. 1500W / 12V / 85% = 150A. 1500W / 24V / 85% = 75A. It's those different amperages that give you the different wire size.
Would I use a 80a fuse for the 24v 1500w inverter?
It's a 75A load so an 80A fuse is too close and you risk nuisance trips. 75A x 125% = 94A so a 100A fuse would be a good choice. 4AWG wire can safely be fused at 100A so you are good.Would I use a 80a fuse for the 24v 1500w inverter?
So instead of a 175a fuse, I'll use a 90a fuse on a 24v 1500w inverter correct?24v fuseing is the same as 12v just that your amperage is half what 12v would be for the same wattage. If you are calculating amps the fuses are the same as they would be for 12v at the same amperage.
Using the formula, does this PDF look right?1500W / 24V / 90% x 1.25 margin x 1.12 ripple factor = 97A
Does this look right? I over gauge by 1:It's based on amperage. 1500W / 12V / 85% = 150A. 1500W / 24V / 85% = 75A. It's those different amperages that give you the different wire size.
Yes I've corrected from your post above thank you so much.You still have wrong wire size for 1200w and 3000W.
Using the formula, does this PDF look right?
Actually they are Battle Born batteries, not that it really matters.The pictures show a SOK battery
As I stated earlier, 1500W at 24V can be 75A so the 115A fuse works fine. I suggested 4AWG for the 75A load. A 115A fuse is fine for 8AWG or thicker.That shows 115A fuse for 24V, 1500W
Why 2/0AWG for a 75A load?How about 2/0?
Actually they are Battle Born batteries, not that it really matters.
Why 2/0AWG for a 75A load?
So 6AWG is just under 3%. I suggested using 4AWG for 75A so well under 3%. So again, why suggest 2/0AWG for 75A when 4AWG, even 6AWG gets you under 3% VD? I'm a big believer is using larger wire than strictly needed but no need to severely over do it.If 10' away, 20' round trip, 0.008 ohms x 75A = 0.6V drop, 2.5% of 24V