Hedges
I See Electromagnetic Fields!
- Joined
- Mar 28, 2020
- Messages
- 20,683
I assume your talking about one like this and you’re right, they are all over eBay: https://www.ebay.com/itm/3838823988...624&ssuid=&var=&widget_ver=artemis&media=COPY
While that will work, 240V in and 120/240V out so it distributes load evenly across the two inverters, any of these transformers is far from "ideal". They are optimized for cost, while carrying a tolerable no-load current. Your inverter may or may not be happy with that (more battery drain, and a few amps out of phase current to source and then sink, an "inductive" load.) Note the current waveform that is not a sine wave, more like a Hershey's kiss. And 7x greater than in my previous posting:
transformer excitation current - isolation transformer used as auto-transformer
So you think you can backfeed a transformer secondary, either as step-up or as auto-transformer? Turns out these things aren't so ideal and reversible as one might expect. It isn't just the greater inrush (primary is often wound outside secondary to reduce inrush current), but also idle current...
diysolarforum.com
What you want is closer to an ideal transformer/inductor, with low sine-wave current draw. I get decent behavior when I drive a 240V coil with 120V, vs. driving with 240V. I can use an oversized transformer and two 240V primary windings as a 120/240V auto-transformer, but I haven't seen any I can use as 240V to 120/240V isolation transformer while operating the windings at 1/2 of rated voltage. I could do it with two transformers.
Do you have a signal available that indicates grid connected/not connected? If so, you could use an auto-transformer to partially rebalance load on the inverters only when off-grid. It would be disconnected when on grid.