Thanks for trying to answer these questions sir. This is about the last stumbling block for me.1 EGC (Equipment Grounding Conductor) in each conduit.
Sized by the largest circuit in the conduit.
It depends on how you have everything connected together.
But all grounding connected together. And back to the main service panel ground bar.
Length has nothing to do with the size.
Size is based on the largest OCP device that the EGC is protecting.
This is the electrical grounding system. Not lightning protection. That's a completely different and separate system.
I am only pulling one conduit with 4 pair of PV feeds and now with ground(s).
The panel racks will all be bonded together, or I could isolate each inverters racks of panels from each other and run 2 grounds back, one for each inverter and it's 4 associated racks of panels.
I was just wondering what would happen if all panel racks were bonded together (which would be easier) and only one ground (or 2 for the whole bonded rack) was run back and shared between both inverters, would they play nice with that arrangement, since any inductive coupling on the panels would be originating from 2 separate power sources?