Hi
I have 10 265 watt panels with 37.9 volts voc and 9.22 amp's I just received. I can't run them in series because of shade.
What I would like to do is run 2 strings, each in parallel with 5 panels going to one Epever 100 amp cc and one string into another 100 amp epever CC.
Will this cause any problems?
I have been researching and even bought 2 books on the subject and if I understand this correctly then the amps add up and volts stays at 37.9.
Thanks
Greg