Really great discussion going on about my recent "relay for large inverters" video (click here).
But after thinking about it and seeing everyone's input, I am going to redesign my raw cell blueprint to avoid the use of relays and FET based switches entirely. Both work well if sized properly for application, but there are too many potential problems:
3 safe methods for controlling low voltage disconnect of large inverters:
But after thinking about it and seeing everyone's input, I am going to redesign my raw cell blueprint to avoid the use of relays and FET based switches entirely. Both work well if sized properly for application, but there are too many potential problems:
- Some relays are not rated for continuous duty
- Relay kickback issue, which can destroy BMS if no fly back diode
- Adds unnecessary complexity
- Capacitive load issues. If relay is sized properly, it shouldn't be an issue. But you need to make sure that relay is huge.
- Increased idle consumption
- Inrush surge can cause damage to fets. Victron recommends not using them with inverters anymore for this reason
- FET's running capacitive loads can't be that great (from what I am reading right now. those spikes will damage them eventually. even if they do not fail, you may get a leaky fet)
3 safe methods for controlling low voltage disconnect of large inverters:
- Using a high quality inverter with relay input. This way you will never need to worry about switching large currents. Use a BMS or other form of logic control system to control the inverter.
- Increase the voltage of your battery bank to reduce the current requirement of your inverter, then run a standard 100-300A BMS. A 100A 48v BMS is small and can easily power a 4500W inverter. A 300A 48V BMS is a bit larger, but can run a 13,500W inverter.
- Run BMS in parallel. But! Not in a single bank. That can cause other problems. You will need to make multiple battery banks with their own BMS, then parallel the battery banks together for a larger current capacity.