400bird
Solar Wizard
Can you explain what happens when the XW shuts down? There should be an alarm/warning logged, if the inverter was unhappy with something.
Odd, can you post all your settings?When working with Schneider TS, he had me put the slave inverter in standby and just try the master. Nothing really happened. The generator was running but the inverter wouldn't ramp up and cutout like before. It just wouldn't accept the incoming charge from the generator at all, where as
before it would run up to 60-70 amps and drop back to normal operating mode.
Ouch, what a bummer. Sorry to hear that.During the night the system reached it's cutoff point of 50 volts and shut down completely.
I'm sure the batteries will be fine, the limiting factor is likely your charger.So this morning after jumping through hoops to get one of the six batteries to come off protection mode, they are all taking a charge from a remote battery charger run off my generator. Set at about
10 amps, I'm not sure how long it will take to get batteries charges up. Would it be safe and advisable to up that amperage?
You can power it from a wall wart or the XW in standby.I don't think I can get into InsightHome to check and tweak these settings until batteries are charged and system is running again.
I wonder if the display lags behind actual charge current and while the highest displayed current was 60-70, maybe it got closer to 90 and the generator voltage started to sag. Then the inverter cut charging.The 60 to 70Amps value is presumably from the Inverter display(s) and is charge amps going to the batteries. So are you saying BOTH inverters are trying to charge at 60+amps or is that each inverter indicates 30 to 35A and you are doubling it since there are 2 inverters?
60Amps at 56V = 3,360W
The Honda generator is rated at 5,500W max continuous output which translates to 98A at 56V.
With 2 inverters, each would only be able to support <48A of charge current in the best case scenario.
Try using the slider or a slightly different number.I tried lowering the specs for Bulk Termination and High Battery Cutout and when I hit apply they usually turn green when accepted. They turned red.
I'm glad I suggested the sliders, I wasn't sure what the min/max in those was.Good advice 400bird, High Battery cutout was 65, tried to get to 56.6, lowest it will go is 58.
Bulk Termination Voltage is 54 and that is the highest it will go so 56.2 is not possible.
I'm about to give the generator a try with these new tweaks.
Gold start! Keep playing until you get it working like you want.So the good news is the inverters are staying on. The Master shows 27.5 amps and the Slave shows 27.9 amps. InsightHome shows
3.3kw coming from the generator.
Thoughts?