@Carlos_Sol-Ark, same deal for AC? I.e., best practice to have a separate disconnect if you're feeding PV AC into the gen terminal?
It is still recommended to have a disconnect for serviceability for AC coupled solar, but it is really up to local AHJ and preference at that point. When AC coupled systems are disconnected from the grid we will begin to frequency shift automatically and the microinverter output power will stop, but it doesn't hurt to have a reliable means of disconnect for safety outside of the GEN breaker for the 12K. The 15K however does not have an individual GEN breaker so keep that in mind during installs.
 
Depends on where they are wired. Microinverters on SolArk output or generator port, and SolArk looks like grid to them.
 
Here is my solution to a single large battery, and the dual 200A breakers. A 2/0 jumper:

IMG_4334.jpeg
 
I was wondering about that. My battery has a maximum discharge of 300A. As long as 100A goes to the second breaker, I'm golden.
 
I was wondering about that. My battery has a maximum discharge of 300A. As long as 100A goes to the second breaker, I'm golden.
And how many Amps can that Single wire coming up handle ?
 
The single wire is 4/0, 445A. The jumper is 2/0, 330A.
I don’t think those values are correct, those wire sizes are rated for significantly less current from what you think.

Edit: I stand corrected, those values appear correct.
 
Last edited:
BatterycablesUSA UL listed cables:

For use as battery cables:
SAE J-378 Table of Allowable Amperage for conductors 50V or less with 105C rating
Gauge Amps Outside of Engine Space Amps Inside of Engine Space
6 120 102
4 160 136
2 210 178
1 245 208
1/0 285 242
2/0 330 280
4/0 445 378
 
12,000W/50V = 240A
240A / 90% / 80% x 1.25 x 1.12 = 373A

4/0 60C: 300A 75C: 360A 90:C 405A ampacity in free air

4/0 cable doesn't quite meets requirements using 90 degree C insulation, standard 80% of rated ampacity, assumed 90% efficiency, an my +12% for "ripple factor"

A couple tweaks to ratings and assumption, and it might just squeak by.

All good.
 
Last edited:
12,000W/50V = 240A
240A / 90% / 80% x 1.25 x 1.12 = 467A

4/0 60C: 300A 75C: 360A 90:C 405A ampacity in free air

4/0 cable doesn't quite meet requirements using 90 degree C insulation, standard 80% of rated ampacity, assumed 90% efficiency, an my +12% for "ripple factor"

A couple tweaks to ratings and assumption, and it might just squeak by.
The 15k can only pull 275A continuous from batteries
 