thanhrodke
New Member
- Joined
- Sep 8, 2022
- Messages
- 131
Howdy all!
I currently have 32 455W panels in two 8S2P arrays into two EG4 6000EX inverters. So that's about 400V name plate VOC, which is just under 500VOC at -10F, the coldest temps in my area.
The inverters have 7,500 watt MPPTs at 500volts which is 15 amps. With the 8S config, I get about 325-350 volts peak on hot days, and with the 16 amp limit, that's about 5,500 watts. Across two inverter/chargers, I can get a peak power of about 11kW out of the two MPPTs, even though I have about 14.5kW of solar power.
I have two spare 6000EX inverters, and am curious if you can just tie all solar to a common set of bus bars, then feed any number of inverter/chargers from the bus bars? On a clear day, it could be an additional 12-15kWh of power, or 25% more than I am currently capturing.
I don't need the AC power from the extra two inverters except on the weekends when I may be running multiple heavy motor loads (3-5hp). On weekdays, I could simply turn those inverters about mid-morning to better capture the maximum available power from the panels, then shut them off mid-afternoon. Otherwise, on cloudy days, when I may only be generating 3-5kW of power, I could just leave the two extra inverter-chargers turned off.
My current plan is to separate each 8S2P array, and end up with four separate 8S arrays feeding the four inverter/chargers, but then got curious about being able to just bus bar all the solar, and then it would not matter how many inverters I had turned on or not, the cabling would all be the same.
Anyhow, just wanted to ask the forum if this was even possible. I can't say that I understand the interaction between an MPPT and the panel array.
I currently have 32 455W panels in two 8S2P arrays into two EG4 6000EX inverters. So that's about 400V name plate VOC, which is just under 500VOC at -10F, the coldest temps in my area.
The inverters have 7,500 watt MPPTs at 500volts which is 15 amps. With the 8S config, I get about 325-350 volts peak on hot days, and with the 16 amp limit, that's about 5,500 watts. Across two inverter/chargers, I can get a peak power of about 11kW out of the two MPPTs, even though I have about 14.5kW of solar power.
I have two spare 6000EX inverters, and am curious if you can just tie all solar to a common set of bus bars, then feed any number of inverter/chargers from the bus bars? On a clear day, it could be an additional 12-15kWh of power, or 25% more than I am currently capturing.
I don't need the AC power from the extra two inverters except on the weekends when I may be running multiple heavy motor loads (3-5hp). On weekdays, I could simply turn those inverters about mid-morning to better capture the maximum available power from the panels, then shut them off mid-afternoon. Otherwise, on cloudy days, when I may only be generating 3-5kW of power, I could just leave the two extra inverter-chargers turned off.
My current plan is to separate each 8S2P array, and end up with four separate 8S arrays feeding the four inverter/chargers, but then got curious about being able to just bus bar all the solar, and then it would not matter how many inverters I had turned on or not, the cabling would all be the same.
Anyhow, just wanted to ask the forum if this was even possible. I can't say that I understand the interaction between an MPPT and the panel array.