Hey all, I need some advice on solving a voltage drop issue that has emerged due to some planning and provisioning mistakes which I made.
The layout...
Shipping container has my batteries, scc, inverter and the array is just out side the container.
21.1 kwh lifepo total capacity
5kw 120v inverter
5kw array
The cabin with all the big loads is about 200' away.
The geography and future development plan forced the distance. The mistake was running 120v over 10/3 solid copper for the main line from the inverter to the main cut-off and breaker box.
Originally the load was going to be no more than about 10a. I should have gone with a higher awg and 240 from the start. But, alas, I didn't.
The Inverter has been upgraded from 3kw to 5kw and the peak load now is about 25 amps over that 120v 200' run now that the cabin has a new induction cook top, electric kettle, fridge, and mrcool minisplit.
Some guests use everything at once because they don't like to read... I guess.
Bottom line is that lights dim a lot when the induction cooker kicks on. They dim less when the heat is on. I need to reduce the voltage drop somehow.
I have considered...
1. Split phase 240v with a sungold 4kw inverter - replacing my current 5kw 120v. Then splitting the two big loads onto different 120 lines.
2. Sending 240v from a new 240v single phase inverter to a 4kw step down transformer and 120v into the breaker box as it's currently wired.
Running bigger awg wire is not an option due to geography, hassle and cost of trying to get expensive bigger wire through 2" conduit with curves that contains existing wire. Heck, the wire would cost hundreds alone.
What would you do ?
The layout...
Shipping container has my batteries, scc, inverter and the array is just out side the container.
21.1 kwh lifepo total capacity
5kw 120v inverter
5kw array
The cabin with all the big loads is about 200' away.
The geography and future development plan forced the distance. The mistake was running 120v over 10/3 solid copper for the main line from the inverter to the main cut-off and breaker box.
Originally the load was going to be no more than about 10a. I should have gone with a higher awg and 240 from the start. But, alas, I didn't.
The Inverter has been upgraded from 3kw to 5kw and the peak load now is about 25 amps over that 120v 200' run now that the cabin has a new induction cook top, electric kettle, fridge, and mrcool minisplit.
Some guests use everything at once because they don't like to read... I guess.
Bottom line is that lights dim a lot when the induction cooker kicks on. They dim less when the heat is on. I need to reduce the voltage drop somehow.
I have considered...
1. Split phase 240v with a sungold 4kw inverter - replacing my current 5kw 120v. Then splitting the two big loads onto different 120 lines.
2. Sending 240v from a new 240v single phase inverter to a 4kw step down transformer and 120v into the breaker box as it's currently wired.
Running bigger awg wire is not an option due to geography, hassle and cost of trying to get expensive bigger wire through 2" conduit with curves that contains existing wire. Heck, the wire would cost hundreds alone.
What would you do ?