Talked to tech support at signature, but was told to install the 5k split phase and that would fix the issues. So I will order that and give it a try. Not to familiar with it and currently reading up on it since it talks about min max delta on the legs.
This is what confuses me some as that is not a whole lot of power:
and the power difference between the two split phases can not exceed 2.5kW.
THIS IS A PRE-ORDER ITEM WITH A 4 WEEK LEAD TIME Signature Solar now offers the latest US Split Phase Auto Transformer by Growatt. This autotransformer takes Single Phase 240Vac (L/N) electricity output and creates true Split Phase 120Vac/120Vac (L/L/N). This addition to our line sheet increases...
www.signaturesolar.com
Perfect for use with the Growatt 5kW ES off-grid inverter, which can be purchased:
Here.
- ATS-US comes with a built-in transformer
- ATS 5000T -US has a maximum sum of L1-N and L2-N simultaneous output is 5000VA
- Please note, the maximum imbalance between L1/L2 is 2500W (E.g. 1250/3750 L1/L2) purchase two if you believe your needs will exceed
- Maximum continuous power is 5kW for energy storage
- PLEASE NOTE THIS IS NOT AN AUTOMATIC TRANSFER SWITCH. THIS PIECE OF EQUIPMENT HAS BEEN CREATED FOR THE U.S. MARKET AND THAT FUNCTION HAS BEEN REMOVED.
FULL SPEC / OVERVIEW
MANUAL / QUICK START GUIDE
UL CERTIFICATE
*The rated power of secondary side L1-N and L2-N can be up to 5kVA respectively, and the power difference between the two split phases can not exceed 2.5kW.