diy solar

diy solar

EG4 6000XP Neutral-Ground Bonding

Thoughts on this configuration...

View attachment 206440
Completely off-grid? Yes, this is totally viable and looks good to me.
Assume you need to add an EGC from batteries to the main panel ground bar. Still think it’s odd you can’t land the PV ground in the inverter. Just not making sense to me.
I understand where you are coming from because it doesn't make sense to me either. I won't claim to know how every circuit on the inverter is drawn out, and why certain things work the way they do, but I know through hours of troubleshooting and consulting with the R&D team, that moving it has resolved that flicker issue for a lot of customers.
 
I do not have experience with the tesla charger but I do know it has circuitry the checks for the NG bond. As far as I know it should work with your set up.
I have a 6000xp setup with 2 eg4 batteries to go off grid charging the Tesla. It work great for 2 weeks but when I updated the 6000xp it gave me the 2 red flashing light in the Tesla charger which I think indicate no NG bond but I did have the settings 26 which NG bond enable. Still try to get it figure out what’s going on. anybody have this problem?
 
what about on-grid?
For on-grid, the NG bond should be in the Main Breaker Panel and the relay in the inverter should be disabled (Never create a bond).

Frankly, I don't understand why the 6000XP has a bonding relay. I would not use it in either an on-grid or off-grid mode. I would always do the bond outside of the inverter. (A bonding jumper is way more reliable than a relay)
 
The reality is, even systems that do dynamic bonding well has to make assumptions about whether there is a bond on the AC in. I do not know of anything on the market that can handle AC-in without bonding sometimes and AC-in with bonding other times. It could be done with modern electronics that detect if a bond exists or not, but I am not aware of any current inverter product with that capability.

So true!!! The 6000XP has a design center of stationary installs. Trying to apply it to mobile is a little bit of a square peg and round hole situation.
I have grid power backed by an unbonded gas generator through a 4 wire cord and plug to the main panel using a manual generator interlock kit. I want to replace it with a portable inverter. I bought a TP6048 that bonds the output when input ac is off. I think my choices are: 1. go inside the TP6048 and find a way to disconnect the bonding relay (and the warranty), 2. substitute a 6000xp set to no-bond, 3. move my priority circuits out to a new unbonded panel connected through a three conductor transfer switch and bond at the inverter (either one). Am I missing something.
 
This is a really good explanation. Very detailed.

The only thing I would add is Grounding in general. No matter what scenario you are in Off Grid or Grid tied you always need a ground. I know being Grid tied you will have one usually but Off Grid we see so. many ungrounded systems and that is so scary because you can or will become the ground at one point.

So please always have a actual Ground no matter what.
I know this is an old thread but have a question:

@Markus_EG4 or anyone else who really understands this stuff:
How do you recommend grounding in a grid-tied scenario?

@timselectric who is the grounding guru on this forum told me
"You can add a ground rod if you are never going to connect to grid. If you are [grid-tied] I would not recommend it."
https://diysolarforum.com/threads/d...ror-f08-gfdi-_relay_failure.74146/post-939258
 