Looks great
@automatikdonn ! ?
I love the use of the overvoltage protection relay to drive a 240V contactor coil by switching one leg only - great idea and it simplifies the wiring a bit too. Thanks for putting the video together and sharing, I plan to do the same within the next couple months - I've got another project that I'm taking care of, and I also want to finish up the conductor/conduit schedule, as well as physical layout.
A few questions:
- Looks like you're pulling the 240V off your L2 IN for your contactor, if so:
- Are you using a ferrule to get two conductors into one slot on the contactor input, or does the contactor have multiple terminal connections?
- If you're using a ferrule, do you know if this is code compliant?
- Do you have any plans to independently fuse the coil circuit (specifically a fast-blow, lower amperage fuse)? Right now the coil appears to be on whatever dual pole fuse that your GW #1 AC OUT shares
- Any chance we could get a peek into your 18 space DIN enclosure ('Inverter Disconnect Service Panel')?
- Is your 'Switching Logic Enclosure' ground buss something you added, or did it come with?
- Do you plan on adding an additional neutral buss to this enclosure for when you add the bonding relay/contactor?
- Did you bond your DIN rail to ground in both/either enclosure? Are any of the latch-on DIN devices grounded through their connection with the rail?
- Most importantly: Do you have access to an oscilloscope, or some high sampling rate voltage measurement device, that is capable of measuring the L1/N & L2/N voltage output of the contactor during the 'lost neutral' failure scenario?
- I know the overvoltage protection relay has a 0.1s disconnect time, and that's a bit of an eternity in an of itself, especially when you stack that with the time to physically de-energize a physical contactor coil.
- If you don't have an o-scope, you may be able to hillbilly simulate this with a regular incandescent bulb. From there, you could build confidence, and perhaps even upgrade to a 120V appliance that you don't particularly care about (both resistive and inductive load).
- Is there a reason you (appear to be) running the AT N output through a single pole breaker (within the 'Inverter Disconnect Service Panel')?
- It looks like you're using a DIN terminal block in your 'Switching Logic Enclosure' to combine neutral conductors
- Could you confirm this is 2 conductors in, 3 conductors out?
- Are these two neutrals coming from the two ATs, respectively? (I'm assuming these are the outputs from the two single-pole neutral breakers within the 'Inverter Disconnect Service Panel'?
- Are these all fed into the same terminal connection?
- It appears your DIN terminal block is two blocks, side-by-side. Are they bussed together with a screw-on bar?
- Could you link to this part you used?
- It looks like you're running ground from the 'Main Service Panel' through GW #1, is that correct?
- I'm not sure a 50A rated contactor will be able to handle fault current for an upstream 50A breaker - are you using a 40A DP breaker for your GW #1 AC out, or do you plan to parallel contactors to be able to flow this fault current?
1. There are not any ferrels on there at the moment, this setup is temporary. There are some problems that need to be addressed. This was the cheapest way for me to test the setup I had in mind. There should be a fast blow fuse on the contactor activation circuit, but I was tired of waiting on parts.
2. Sure, I can get some photos or take another video. To be honest though, these boxes are likely to go to the trash bin or to some project that doesn't carry critical loads. I am going to order a UL listed steel box for both of the parts in the 18 din boxes to go into. I just didn't know what size I needed, so now that I have a closer idea of right would look like, I will get something more code compliant.
3. Nothing comes with ground buss bars. It boggles the mind why they aren't included ( I guess they could say that everyone wants something different). The neutral auto connect circuit will need a buss bar, but I have to find a way to isolate it. I am searching for parts, but coming up short.
4. The din rail is grounded with a ground connector for din rails. When I get a full parts list together, I will include this.
5. I do have a scope. I just got a hantek that I have been itching to take out and use. I should even be able to hook it up to a computer so I can get some screen recording to post.
6. You are correct. The neutral out is on its own 30 amp single pole breaker. I have breakers at every single input and output. I guess I could have got away with just killing the input to service them, and I guess it's just an old habit to have disconnects for all inputs and outputs. The input is on a double pole and output on a single pole. Should I be doing this different?
7. Yes, I am combining the neutral outputs at the terminal block. The connection between the two is not a screw down, but it is UL listed. It's a dinkle 100amp terminal block.
There are 3 outputs, because at this point in the circuit the inverter outputs are not yet combined. I think this is very likely to change, but for the current setup I would not be able to fit the required wire size to fit in that tiny box. Once the conductors are combined it drives up the current size. So for my setup (15kw) I would be looking at #1 wire (150 amps due to surge capacity). I am trying to find a way that monitors the circuit properly that does not combine anything. This would also drive up the required contactor size. It has some problems I can't quite put my finger on. For instance if I flip the output from the neutral on and off really quickly things never seem to normalize and the meters read 60 volts instead of 120. I checked with a volt meter and the voltage overprotect / underprotect devices are correct. I just don't know why. Also it acts funny when I simulate the failure of just one AT. Again I don't know why. Maybe someone can help point me in the right direction.
8. There is also a path the comes in direct from the main service panel that is connected in the disconnect box. Not sure if that is right or not.
9. These particular contactors are rated at 50amps. All of the connectors say 63 amps, so that rating is a full 50 amps. However they are garbage. Already broke two of them and one came with a bunch of rattles inside. A proper UL listed contactor is a requirement IMO. This is a critical function, so no reason to cheap out on this device. Thankfully my listed contactors showed up today... However they are way too big to fit in these tiny boxes.
Hopefully I answered all the questions fully. Let me know if you want to see anything else.
Also I now have a panel to actually pull power from (inverter load panel). I also finally got a battery running so I can turn the system on and start the testing.
Apologies to everyone waiting on the full answer to the OP question. I want to be through before publishing a full parts list and completed chart for how it all works. I think at the least having two AT's massively reduces your risk if you decide to move forward without this protection circuitry in place.
More to come