Not to overload you with too many instructions, but some settings to check:
Setting 01 I see the default is Utility First - this would answer my question as to why the MPP was in by-pass, Change it to SbU (solar-battery-Utility)
Setting 16 set the charging priority to OSO (solar only) - just while we sort out the overload condition.
Setting 18 set to bOF will turn off the alarm beep (if you like)
Setting 23 set to "byE" this enables the unit to by-pass if the battery is not sufficient to run the loads.
Try these settings and I will watch for your report back.