It's not crazy, it is what happens if the ground reference is not at zero.
That is not an inverter problem but a systems problem. I know, I had one inverter that was doing exactly what you showed, output voltage would move from 112V to 126V and I had pulsing lights at the time.
I'm pretty certain my system has been corrected. I was experimenting and testing , step by step to observe various system behavior after reading thru all the problems you read about here. Most people blame the inverter, but in reality it is systems/design problem. I wanted to test a few things, see the results and then change the next thing and see results in the next tests. Part of the learning process and how to understand why you see the abnormalities.
How is this system bonded and how are the EGC's ran? Have any diagrams? One or a pair of inverters?
I have a single EG4 6500 - I have spaced out the equipment and have it ready to add the second 6500 as that was the original design. I am not sure at this point if we will need the extra 6500 for additional load or just additional MPPT's but that is a separate discussion.
The input AC side of the EG4 is wired to a generator outlet on the outside of my basement via 8 awg thhn. The generator is currently not connected but will be used if needed for those prolonged cloudy days and snowy winters as required.
The output AC side of EG4 is connected to a 100 amp sub panel through a 60 amp breaker via 4 awg thhn. Upstairs is our main panel - our main panel is connected to (2) six (6) outlet transfer switches. All of our used circuits from the main panel have been presented on the two transfer switches and balanced according to loads. The 240v circuits in the main panel have been abandoned as we discontinued use of those circuits, exchanging our electric dryer for gas.
The transfer switches allow us the ability to flip each circuit between grid power and solar power independently. This was critical for us and found to be very valuable in the beginning as we originally didn't have enough panels to power our needs.
At this time ALL circuits are flipped to Solar and we have no loads running on the grid, once the bugs are worked out we will be disconnecting that service.
The sub panel below feeds the two transfer switches with 4 awg thhn.
The neutral ground bound lives is the main panel and the new firmware in the EG4 disabled the internal neutral ground bond in the inverter.
www.reliancecontrols.com
The problem is holding the leads in your hands while moving around. The connection between the measuring point and your leads changes, this changes the resistance and you see the voltage change. If you want true readings, you need a solid connection such as a clamp end to ensure the connection remains constant.
As shown in the video part of it is my fumbling trying to hold everything and the leads tight, however that is not the case for the wild swing as the leads are tight and the swing still occurs, then when the EG4 is disconnected I get a solid reading, still holding the leads. I am not sure how I could have recorded the video otherwise as this was at the request of SS, they wanted to see the PV voltage both before and after resetting the input. Anyway I understand the point, but was limited.
Not unusual, Will even had a recent video about this.
Thank you