PV Input issues:
(1) I have to restart or power off the inverter daily then power it back on in order to get the proper solar power from PV1. As as example to today, this morning PV1 was showing a measly 100+ watts of power coming in, I knew this wasn't correct, although the sun just crested the mountains it was not hindered by any clouds. Powering off the unit and back on the input on PV1 jumped to over 850 watts and immediately began charging the batteries. A few hours later I am now pulling in 2.58 kW and here shortly it should top out at 3.98kW. If I don't power cycle the units it won't properly power the inverter or charge the batteries.
(2) I have also noticed this in the afternoon, the charger will charge the batteries to to near 96% or so and then clip (I believe that is the proper term) the PV input to match (or just below) the inverter output and the batteries stay in a discharge state ~2.80 amps and never reach 100%. I will have full sun and the unit will only show maybe 800w or so coming and the batteries should be fully charged but are not, I then test the PV input by turning on a space heater or two and the PV input will immediately jump to several kW to meet the load of the heater. Again if I power cycle the inverter the PV input is not clipped at the inverter output rate and the batteries quickly reach 100% charge and then go into standby as they should.
I can not trust this inverter charger to properly charge the batteries and maintain our system.
I also have random issues with lights flickering, They don't flicker all the time and seems no rhyme or reason when they flicker, they may flicker when on battery or solar power, sometimes they flicker and other times they do not.
I also have an issue where I occasionally have to run the generator to charge the batteries, several days of low or no sun. When I do, the generator will power the loads however the inverter switches the battery from charging to discharging. I would like to be able to run the generator to charge the batteries as required in these situations.
I have contacted SignatureSolar on these issues and have yet heard back from them. The generator issue has been open since January 30th, 2023 and PV issues have been open since 2/23/23.
My plan was to add a second unit in parallel this spring, at this point I have lost confidence the inverter, EG4 and SignatureSolar.
(1) I have to restart or power off the inverter daily then power it back on in order to get the proper solar power from PV1. As as example to today, this morning PV1 was showing a measly 100+ watts of power coming in, I knew this wasn't correct, although the sun just crested the mountains it was not hindered by any clouds. Powering off the unit and back on the input on PV1 jumped to over 850 watts and immediately began charging the batteries. A few hours later I am now pulling in 2.58 kW and here shortly it should top out at 3.98kW. If I don't power cycle the units it won't properly power the inverter or charge the batteries.
(2) I have also noticed this in the afternoon, the charger will charge the batteries to to near 96% or so and then clip (I believe that is the proper term) the PV input to match (or just below) the inverter output and the batteries stay in a discharge state ~2.80 amps and never reach 100%. I will have full sun and the unit will only show maybe 800w or so coming and the batteries should be fully charged but are not, I then test the PV input by turning on a space heater or two and the PV input will immediately jump to several kW to meet the load of the heater. Again if I power cycle the inverter the PV input is not clipped at the inverter output rate and the batteries quickly reach 100% charge and then go into standby as they should.
I can not trust this inverter charger to properly charge the batteries and maintain our system.
I also have random issues with lights flickering, They don't flicker all the time and seems no rhyme or reason when they flicker, they may flicker when on battery or solar power, sometimes they flicker and other times they do not.
I also have an issue where I occasionally have to run the generator to charge the batteries, several days of low or no sun. When I do, the generator will power the loads however the inverter switches the battery from charging to discharging. I would like to be able to run the generator to charge the batteries as required in these situations.
I have contacted SignatureSolar on these issues and have yet heard back from them. The generator issue has been open since January 30th, 2023 and PV issues have been open since 2/23/23.
My plan was to add a second unit in parallel this spring, at this point I have lost confidence the inverter, EG4 and SignatureSolar.