EG4 18kPV issues - turning on and off repeatedly at sunrise and sunset

I have the same issue with the lux 12k us

Firmware FAAB-1717

Where it would turn off and on 12 to 15 times in the morning every minute or so.

Also happened once in the evening.

I've changed the Start pv voltage from 140 to 250v to see if that remedies it.

Seems like it could be a Firmware issue.
Or have something to do with the vmp voltage of the pv array.
Yep, same. I bumped up the PV start voltage and tada

Note: This was a problem before FAB-1717 for me
 
I get the same on/off at sunrise and sunset on my MPP Solar LV2424 and just thought it's normal. Most mornings it doesn't wake us up but the relay clicking does get annoying. It's been doing thos for over 3 years. It's almost an alarm clock that competes with a rooster if one is around.
Is your inverter connected to the grid? Or a battery?

If there is no Ac input or battery it is normal for the inverter to try to start and fail as the sun comes up. But it would be great if MPP could add an adjustable solar start voltage as well.
 
Is your inverter connected to the grid? Or a battery?

If there is no Ac input or battery it is normal for the inverter to try to start and fail as the sun comes up. But it would be great if MPP could add an adjustable solar start voltage as well.
I'm connected via battery.
 
I have the same issue with the lux 12k us

Firmware FAAB-1717

Where it would turn off and on 12 to 15 times in the morning every minute or so.

Also happened once in the evening.

I've changed the Start pv voltage from 140 to 250v. edit it seems to have fixed the issue.

Seems like it could be a Firmware issue.
Or have something to do with the vmp voltage of the pv array.
So the lux 12k exposes the solar voltage startup setting to end users whereas the eg4 doesn't?
 
So the lux 12k exposes the solar voltage startup setting to end users whereas the eg4 doesn't?
I am a dealer with my own code. So I have access to those settings. On the app. But anyone should be able to adjust it at the inverter. Under settings-advanced

20240214_125918.jpg
 
Last edited:
We know its adjustable on the 18kpv, but is it adjustable by the end user? My understanding is that it is not!
Correct me if I am wrong.
Yes it is on the EG4 18Kpv, but can only be accessed on the unit by the end user.
 
We know its adjustable on the 18kpv, but is it adjustable by the end user? My understanding is that it is not!
Correct me if I am wrong.
It can be adjusted at the unit! , and by your distributor/installer!
 
It can be adjusted at the unit! , and by your distributor/installer!
And without a secret password?
It sounds like some hysteresis needs to be programmed into the controls. Like a time off timer so things dont change when pv power input is on the edge of the setting.

Is the inverter manual being updated as the firmware changes?

It sounds like this inverter has potential after the bugs are worked out. And they drop the price. Thanks to the test subjects that have had to endure the issues.
 
And without a secret password?
It sounds like some hysteresis needs to be programmed into the controls. Like a time off timer so things dont change when pv power input is on the edge of the setting.

Is the inverter manual being updated as the firmware changes?

It sounds like this inverter has potential after the bugs are worked out. And they drop the price. Thanks to the test subjects that have had to endure the issues.
The default password on the display is just 0000 there has already been alot of bug fixes and luxpowertek seems to be quite responsive when it comes to recognizing and addressing bugs.

This inverter has great value when comparing it to the sol-ark 15k
Wich is comparable in specs

But yes a lower price is always welcome as long as the quality stays.
 
This inverter has great value when comparing it to the sol-ark 15k
Please elaborate....

The Sol Ark 15K is now down to about $6500. The 18KPV is $5200

The Sol Ark does 15KW continuous, the 18KPV does 12KW continuous.

$ per KW of AC output they exactly the same.

It appears that the price of both units is dropping.

Personally I need more than one 10KW+ unit. The huge amount of pass through doesn't really make sense for me. I'm not trying to eliminate my main panel. I already have subpanels, three of them besides the main panel. For bigger houses I think this is pretty common.
 