RuiXU battery experiences

Is everyone still happy with the Riuxu batteries? I'm considering the 10-battery rack to pair with a Sol-ark 15K.

Any issues getting comms working properly?
 
Is everyone still happy with the Riuxu batteries? I'm considering the 10-battery rack to pair with a Sol-ark 15K.

Any issues getting comms working properly?
The manual is quite thorough, 28 pages with tables, and illustrations. It puts the EG-4 stuff to shame, very professional looking with little if any Chinglish, easy to understand.

My only problem is, at the time I couldn't find a patch cord in my box of crap that was the right length for some reason, they were all either 25ft or 3ft long. Just buy something from amazon of the optimal length, I like the flat stuff

To an earlier post, RS-485 is a 2-wire serial protocol, basically an asynchronous protocol like RS-232/422 but over a shared differential bus instead of dedicated transmit/receive pins to a ground. It's used a lot for probes and other devices that get polled, and if memory serves theoretically supports 256 devices on a single pair, though most chipsets limit it well below that, like 40 or so.

RJ-45 is the form factor of the plastic 8 conductor cable end used by most network cables and sockets (Ethernet). The RUiXU manual describes everything you might need. Pins out 1/2 and 7/8 for RS485 and 4/5 for CAN, No polarity issues, worked with a straight thru cable to an EG4 18KPV, and it has dip switches that allow you to set the baud rate and the protocol. According to the manual you will want protocol '2' for SolArk, dip-switch 6 on.

NOTE: The CABLE is the same but these boxes are not talking over ETHERNET, the voltages and signaling are totally different.
 
My batteries are performing quite well with 2 X 6000XP’s. Communication works and seems to measure voltage well.

The Ruixu rack is really nice.

My one issue is that I’ve seen my SOC% deviate from my voltage somewhat, but haven’t drilled into it to figure it out completely. Also, they are not on 6000XP’s battery compatibility list, so I wouldn’t expect the communication to work flawlessly.
 
My batteries are performing quite well with 2 X 6000XP’s. Communication works and seems to measure voltage well.

The Ruixu rack is really nice.

My one issue is that I’ve seen my SOC% deviate from my voltage somewhat, but haven’t drilled into it to figure it out completely. Also, they are not on 6000XP’s battery compatibility list, so I wouldn’t expect the communication to work flawlessly.
The SOC may deviate if you ever have a load of less than 0.5A per battery.. Any time less than that will not be recorded as consumption by the BMS. So if you left the inverter on idle for a week, without solar input, the batteries would die with 99% SOC indicated.
 
The SOC may deviate if you ever have a load of less than 0.5A per battery.
I think that is exactly what happened. Phase 1 (complete) of my project was putting in a battery backup system. Phase 2 (next 60 days) is adding the Solar. In wanting to keep my batteries fully charged in case of a power outage, I put the inverters in bypass mode, so I was drawing nothing from the batteries. It took almost 2 weeks, but suddenly the batteries started charging due to voltage. Didn’t understand why.

I do now - Thank you @Detritalgeo
 
Does anyone know if a transformer based inverter like a Sigineer low frequency would pair well with the Ruixu rack batteries? Yes, I know I wouldn't have communication and the warranty voided but I cannot bring myself to purchase one of those "all in one" HF units that probably won't last 7 to 10 years...and besides I want my off grid to run whatever I throw at it. And lets face it, the components in those "all in one" units just aren't heavy duty enough and will wear out faster than a transformer based inverter.

Maybe I need to call Sigineer or Ruixu for the answer but if anyone here knows, then thanks.
 
Does anyone know if a transformer based inverter like a Sigineer low frequency would pair well with the Ruixu rack batteries? Yes, I know I wouldn't have communication and the warranty voided but I cannot bring myself to purchase one of those "all in one" HF units that probably won't last 7 to 10 years...and besides I want my off grid to run whatever I throw at it. And lets face it, the components in those "all in one" units just aren't heavy duty enough and will wear out faster than a transformer based inverter.

Maybe I need to call Sigineer or Ruixu for the answer but if anyone here knows, then thanks.
You are aware that good hf inverters carry a 10 year warranty ?
Also, if you properly size a hf inverter, you won't be having any issues
 
You are aware that good hf inverters carry a 10 year warranty ?
Also, if you properly size a hf inverter, you won't be having any issues
Yep I am aware.

"properly size" see that is part of the problem. That really means:
1) "oversize" for what you will need to run.....which you shouldn't have to do in the first place
2) And still the components inside the HF inverter/charger will be inferior to a transformer based system that can easily run inductive loads and surges....and those components in the HF inverter/charger will indeed wear out much quicker as you have a more complicated cycle that needs to be completed (with more electronic components) to replicate the transformer inverter/chargers

This has been discussed on this form before.....but back to my question (if anyone can shed light)

Does anyone know if a transformer based inverter like a Sigineer low frequency would pair well with the Ruixu rack batteries?
 
Yep I am aware.

"properly size" see that is part of the problem. That really means:
1) "oversize" for what you will need to run.....which you shouldn't have to do in the first place
2) And still the components inside the HF inverter/charger will be inferior to a transformer based system that can easily run inductive loads and surges....and those components in the HF inverter/charger will indeed wear out much quicker as you have a more complicated cycle that needs to be completed (with more electronic components) to replicate the transformer inverter/chargers

This has been discussed on this form before.....but back to my question (if anyone can shed light)

Does anyone know if a transformer based inverter like a Sigineer low frequency would pair well with the Ruixu rack batteries?
A battery is a battery to an inverter
 
Any ideas on the custom cables? I may be planning on purchasing four of the Lithi2-16 in a few months but the wall on which I'll arrange them is a bit over 3.8m wide, if I want to aggregate the pos/neg cables from the batteries to the common bus bars then I'm concerned that the 2m cables that the Lithi2-16 come with may not be sufficiently long to allow for cable management. I'd like a 3m option to be absolutely sure.

Can I disassemble the cables it comes with and use my own custom length cable? Or is there a place like Digikey that might have the connectors from the battery side?
 
Maybe reach out to Current Connected @HighTechLab they are able to create different types of cables. They may be able to help. Not sure they are selling the Lithi2-16's, but I bought my 48volt Ruixu Server Rack batteries from them. Very happy
 
Yep I am aware.

"properly size" see that is part of the problem. That really means:
1) "oversize" for what you will need to run.....which you shouldn't have to do in the first place
2) And still the components inside the HF inverter/charger will be inferior to a transformer based system that can easily run inductive loads and surges....and those components in the HF inverter/charger will indeed wear out much quicker as you have a more complicated cycle that needs to be completed (with more electronic components) to replicate the transformer inverter/chargers

This has been discussed on this form before.....but back to my question (if anyone can shed light)

Does anyone know if a transformer based inverter like a Sigineer low frequency would pair well with the Ruixu rack batteries?
on Friday, May 3, 2024 4:02 PM
I emailed Sigineer Power franklin.sigineer@gmail.com
this was the reponse:
on 05-03-2024 6:40 pm

from
Franklin Chu
Sales

We support modbus and CAN communication, here is the list

Sigineer Power Solar Inverters don’t only work with our own lithium batteries, they are also compatible with 3rd Party Lithium Batteries Models from other brands
—————
Dyness

B4850
———————-
Shanghai PYLONTECH

US2000
US2000PLUS
US3000
UP2500

Shuangdeng Group

SDA10-48100
 
Well, a few posts up from here I asked if everyone was still happy. I ordered, received, installed... and I too am very happy with the 10-rack Ruixu battery rack.

It shipped Fedex freight, arrived in suburban Atlanta in about a week. VERY HEAVY. Very fortunate that my basement had a side-door, so I could wheel everything around on a handcard, one at a time. The 10-rack cabinet is very difficult to move around.

When loaded, the cabinet is very heavy. It's on wheels, but they move very slowly from the very heavy weight. However, the cabinet is well-built, and strong. Assembly is... challenging because the batteries are each very heavy.

Funny story, this is my first time working with server-rack batteries. Previously when watching Youtubers like Will using the hydraulic lift table with these batteries, I'd dismiss the youtuber as clearly not very strong... those batteries can't possibly be that heavy....? Well, it turns out they are that heavy, and a hydraulic lift table would have been helpful. Or a strong pair of teenagers. But I'm 50 years old, so I nominated my wife to help. We got it done, two people to lift each battery. Server-rack batteries are heavy.

Anyways, the cabinet is great. No concerns, even loaded with 10 batteries.

For safety, I added a 200-amp MRBF to every cell, and added a 350a class-T fuse to the entire rack.

It integrated to the Sol-Ark 15K easily. Closed-loop communications works great. So far, charging-wise, with 10kw of solar, I'm raising the SOC from 30% -> 70% each day, in Atlanta in June, while also running two 3-ton Air-conditioners. Wired with a single 4/0 cable to the Sol-Ark, with a Homegrid Bus-Bar on the inverter terminals.

For Testing I charged to 100%, then turned off my solar at midnight. I then ran a normal day with my 2 3-ton air-conditioners, normal living, normal lights, even ran the electric clothes dryer once. At 11:15pm SOC hit 20%, and I enabled overnight charging. So far I haven't yet taken it below 20% SOC.

Is it still recommended to test batteries all the way to Zero? I'm too timid right now.
 

Attachments

  • PXL_20240509_181757746 (2).jpg
    PXL_20240509_181757746 (2).jpg
    199.8 KB · Views: 15
  • PXL_20240612_214100108.jpg
    PXL_20240612_214100108.jpg
    260.9 KB · Views: 13
Last edited:
Well, a few posts up from here I asked if everyone was still happy. I ordered, received, installed... and I too am very happy with the 10-rack Ruixu battery rack.

It shipped Fedex freight, arrived in suburban Atlanta in about a week. VERY HEAVY. Very fortunate that my basement had a side-door, so I could wheel everything around on a handcard, one at a time. The 10-rack cabinet is very difficult to move around.

When loaded, the cabinet is very heavy. It's on wheels, but they move very slowly from the very heavy weight. However, the cabinet is well-built, and strong. Assembly is... challenging because the batteries are each very heavy.

Funny story, this is my first time working with server-rack batteries. Previously when watching Youtubers like Will using the hydraulic lift table with these batteries, I'd dismiss the youtuber as clearly not very strong... those batteries can't possibly be that heavy....? Well, it turns out they are that heavy, and a hydraulic lift table would have been helpful. Or a strong pair of teenagers. But I'm 50 years old, so I nominated my wife to help. We got it done, two people to lift each battery. Server-rack batteries are heavy.

Anyways, the cabinet is great. No concerns, even loaded with 10 batteries.

For safety, I added a 200-amp MRBF to every cell, and added a 350a class-T fuse to the entire rack.

It integrated to the Sol-Ark 15K easily. Closed-loop communications works great. So far, charging-wise, with 10kw of solar, I'm raising the SOC from 30% -> 70% each day, in Atlanta in June, while also running two 3-ton Air-conditioners. Wired with a single 4/0 cable to the Sol-Ark, with a Homegrid Bus-Bar on the inverter terminals.

For Testing I charged to 100%, then turned off my solar at midnight. I then ran a normal day with my 2 3-ton air-conditioners, normal living, normal lights, even ran the electric clothes dryer once. At 11:15pm SOC hit 20%, and I enabled overnight charging. So far I haven't yet taken it below 20% SOC.

Is it still recommended to test batteries all the way to Zero? I'm too timid right now.

I'm jealous! I was contemplating getting the 10 battery rack when I ordered. But I decided on the 6 battery rack. Now I want more batteries!
And yep, these batteries are heavy. My son helped me put these batteries in the server rack. I've been using my Ruixu batteries since November 2023. So about 7 months now. No issues. Every now and then I look through the batteries and connections with a thermal imaging camera to see if there are any hot spots. Nope! None at all. These batteries run cool and the thermal camera shows the temperature is about the same as the background ambient temperature.
 
I'm jealous! I was contemplating getting the 10 battery rack when I ordered. But I decided on the 6 battery rack. Now I want more batteries!
And yep, these batteries are heavy. My son helped me put these batteries in the server rack. I've been using my Ruixu batteries since November 2023. So about 7 months now. No issues. Every now and then I look through the batteries and connections with a thermal imaging camera to see if there are any hot spots. Nope! None at all. These batteries run cool and the thermal camera shows the temperature is about the same as the background ambient temperature.
Straight up, I'm really pissed I didn't start with the 10-unit rack and 5 batteries. I'm building an outbuilding for my power plant. First solar purchase after completion/move will be a 10-rack with at least 4 batteries maybe re-locate the ones from the 6-rack. Or if I have a spare $13K laying around go for the 50KWH gusto. My End goal is two 10-racks, for 100KWH, but I'm in a mixed arrangement with some EG4's.

I also have been using mine since Nov. I note the SOC curve is 2-3% steeper than the EG's. Other than that small capacity reporting difference, they seem to be performing admirably.
 