So I have been in communication with Megarevo via WhatsApp this past week. I think... I think we have a solution for the zero export to ct's. The following was done and I am curious if it works for others:
1. Firmware Version: 1.4.13.BO3D27_20230605.out / LNAV23_20230613.axf
2. Make sure the CT clamped on L1 grid before distro panel (just pick a wire) is the same 120V leg that L1 going into inverter is. Same for L2. The tell here is if your inverter current output is at 0.4A or higher. If its just 0.4A-0.7A and your load is considerably larger, you likely need to plug CT1 into port 2 and CT2 into 1.
3. Sys Setting > Work Mode > Peak Shift
4. Sys Setting > Bat Wake Up > Disabled
5. In your TOU settings
5a. Advanced Settings > TOU 1 > Time > 12am - 6am (change as required) SOC Target 95%
5b. Advanced Settings > TOU 1 > Grid Charge > Enabled
5c. Advanced Settings > TOU 1 > Time > 6:01am - 23:59pm (change as required) SOC Target 35%
5d. Advanced Settings > TOU 1 > Grid Charge > Disabled
6. Advanced Settings > Working Mode > SFC Selldis > Select
1. Firmware Version: 1.4.13.BO3D27_20230605.out / LNAV23_20230613.axf
2. Make sure the CT clamped on L1 grid before distro panel (just pick a wire) is the same 120V leg that L1 going into inverter is. Same for L2. The tell here is if your inverter current output is at 0.4A or higher. If its just 0.4A-0.7A and your load is considerably larger, you likely need to plug CT1 into port 2 and CT2 into 1.
3. Sys Setting > Work Mode > Peak Shift
4. Sys Setting > Bat Wake Up > Disabled
5. In your TOU settings
5a. Advanced Settings > TOU 1 > Time > 12am - 6am (change as required) SOC Target 95%
5b. Advanced Settings > TOU 1 > Grid Charge > Enabled
5c. Advanced Settings > TOU 1 > Time > 6:01am - 23:59pm (change as required) SOC Target 35%
5d. Advanced Settings > TOU 1 > Grid Charge > Disabled
6. Advanced Settings > Working Mode > SFC Selldis > Select