4x agm 100ah to 48v charge/discharge rate?

Wardenclyffe

New Member
Joined
Jul 5, 2023
Messages
6
Location
Texas
i have 4 windy nation 100ah agm batteries in series to 48v what should i set the charge/discharge rate at? for sol-ark 15k

also notice this in the manual
Max A Discharge: Sets the maximum discharge current (A) rate from the batteries → 275A max allowed.
For Off-Grid systems, the battery bank will discharge 120% of this value for a 10 second surge before the inverter faults to
prevent battery damage.
 
Last edited:
100Ah AGM is anemic for a SolArk 15K. You have 50Ah usable.

If it's this one:


1715392075070.png

There's your answers.
 
100Ah AGM is anemic for a SolArk 15K. You have 50Ah usable.

If it's this one:


View attachment 214557

There's your answers.
Yes It's that one.So I could use the whole 275A discharge settings on sol-ark? and 30A charge?
 