I watched the video of Will on the Server Rack of LifePower. It made me very enthusiastic as it always pained me that I have a large Solar System but have to purchase power for overnight consumption and charging the EV when dark. I looked at brand (Enphase) battery options but the price per kW is just horrific. The EG4 Server rack with 30.72kwh (6 Batteries 100ah 48v) is a great value option for me. FYI I can sell back to the grid at ~70% of purchase price.
An Enphase Battery solution of 30kW is $26k (payback period ~80 years)
A 30kW DC Server Rack with Hybrid Inverter 6-8kW is $15k (payback period ~50 years)
I have a 16kW, REC 410 Alpha Pure, IQ8A Micro Inverter Enphase grid tied solar system. I do not plan to add a Generator as the power grid in my area is extremely stable.
I believe I need to add an AC coupling/hybrid inverter with variable frequency to make this possible, but this goes way beyond my knowledge. Can one of you let me know what inverter and diagram (etc?) I would need to integrate a lifepower EG4 server rack to my Enphase system (or if it is a pipedream)?
The Schneider Conext is (I believe) not compatible with Enphase and I got mixed info on the Solark. However, I have very little knowhow in this field and skilled advice is much much appreciated.
https://signaturesolar.com/eg4-ll-lithium-battery-48v-100ahd
-------------#-_----------
I did some research on the Forum and found these posts which are similar to my question. I don't believe they fully explained the solution to my challenge.
Bart1080 Asked
I've a Enphase micro inverter solar system 240v grid tied 12.7Kw Enphase system, Shed Roof mounted. We've had it for 8 months but lots of excess solar power going to waste and would rather self utilize it more with battery backup for power outages to run critical loads with the help of my gen set.
Todd answered:
The Enphase IQ8 inverters can form a microgrid, in combination with their System Controller, which has the automatic transfer switch, the neutral-forming transformer, and the brain of the system. A Sunlight Backup System requires 2 Load controllers, "OR" an Enphase IQ Battery.
The Enphase Sunlight Backup with the Empower switch can do exactly what you want, but it's very expensive relatively speaking. And, Enphase requires the installer to be Enphase Storage Certified, which means their full training program.
No matter what system you decide to go with, the inverter must be sized per code to be equal to or larger than the largest load posted by the system it's connected to. In the case of Enphase, their microinverters are built into their Encharge battery products. They are the inverter. The IQ Battery 3T is limited to 1.28kW continuous, so you're limited to about 5.33A @240V. In your backup-loads sub-panel, the largest load must be < 5.33A. You can add more Battery 3Ts to reach 10.66A, 15.99A, etc. 3 of the IQ Battery 3Ts is equal to 1 IQ Battery 10T, which is 10.05kWh, and installed they run over $10k just for the battery/microinverter box, and cover. To make it all work requires a cellular modem, a Wifi comms adapter, and an Envoy that transmits data from the microinverters and the system controller to the cloud. The cloud connection is a requirement for their Warranty, it won't work without it.
To do what you'd like to do you need to add a backup-loads sub-panel and move the loads you want to run on the battery over to that panel. Just a few of them that you need as critical. If you don't do this, then the sizing of the inverter and the number of panels required will be prohibitively expensive, even when doing it DIY, in order to meet the code.
Best,
Todd
Todd D.
CEO, NC Solar Electric LLC, Statesville NC
I found another comment by Todd on adding DIY batteries to an Enphase system.
Todd answered:
It is possible with inverters certified to UL 1741SA, the "SA" part matters, and they program them with the same type of grid profile as the Enphase.
I also found this thread which is very close to what I'm looking to achieve and goes more in depth on the SolArk. The SolArk 8K is UL 1741SA compliant. Not sure if the 12k/15k are. It is a long read...
Bart1080 Asked
Todd answered:
Best,
Todd
Todd D.
Todd answered:
Sol-Ark 12K + Enphase IQ8 microinverters
Hi All, I'm wondering if it would be possible to supplement a PV DC system connected to a Sol-Ark 12K with a few more panels with Enphase IQ8 microinverters connected to the Sol-Ark's generator inputs?. What do the IQ8s need for them to turn on?. How do you turn them off for RSD...
diysolarforum.com