The BB set and the EG4 set should have the same kwh so I should be able to switch one off to modify or repair while the other one runs fine.Seems like that should give you enough overhead if you had to run solely off the server rack if you had to perform maintenance on the BB batteries.
The autotransformer is interesting. Need to calculate the max load, that may be an easier solution than a second Quattro.I just saw your post. You also have the option of purchasing a Victron 120V-to-240v transformer (https://signaturesolar.com/victron-autotransformer-120-240v-100a/) instead of purchasing another Victron Inverter for your 240V loads. I see you have a Victron MPPT fed by your 2KW solar panels. I would look at the charging data and see how much KW is "really" being provided by your panels, since you just added another 20KWH of storage to your system. I do recommend to purchase the EG4 hub and integrate it into the Victron setup. I have EG4 V1 batteries integrated into my Victron setup and cannot help you with the integration however, I heard that hub suppose to provide the similar capability. I would also connect your EG4 batteries to a laptop so you can monitor them.
Is the ground not currently connected? The current setup w the BBs and Victron was all there before I arrived. I'm just adding the EG4s for now.Don't forget to connect the ground for the Quattro and the charge controller. Would also be good idea to add some kind of cover over that positive busbar even if it is just some clear plastic offset from the busbar.
Also, how did you attach so many lugs to that smartshunt? did you have to remove the washer and lock washer?
If you read back I am about to hook it up but in the photo the EG4s aren't hooked up yet.Where is the negative of those Lifepower4 batteries going? It should be to that smart shunt but I don't see it.
I assumed that fluorescent green cable on the Quattro is connected to the chassis ground bolt on the bottom right side of there but I don't see where that cable is actually going? It looks like it is just rolled up and can't see an end to it.Is the ground not currently connected? The current setup w the BBs and Victron was all there before I arrived. I'm just adding the EG4s for now.
I'm on a rock island so I don't believe the previous owner was able to find ground.Same with that Midnite solar surge protector. I only see positive and negative cables coming out but it has to be connected to a ground as well unless the ground is going out through the wall in that box and can't see it in the pic?
Apparently not according to the previous owner. Her tried to get ground outside but was unable to.Is there no grounding for anything in the entire system including the AC side?
Important! A good grounding system is essential for both safety and lightning protection. The NEC recommends a
ground resistance of 25 ohms or less. The lightning protection industry recommends 10 ohms or less. A thorough assessment of the grounding system is strongly recommended.
Congrats!Hooked them up! No explosions. I do have to figure out the grounding.
Once the EG4 rack comes those will go in the rack, and will run the POS from the rack as it runs now.
The NEG will run to a busbar with all of the other negatives and then copper from the busbar to the SmartShunt.
Thanks for the help Adam!Congrats!
I guess not re the BB connecting.I believe I’ve seen the Cerbo handle different batteries connected to it at the same time. Not sure about the specific GX you have though.
Can the GX connect to the BB batteries?
If you have proper communication set up between the communication hub and the Victron GX, I believe it’s supposed to, but unfortunately I don’t have any direct experience with the communication hub and it’s integration into Victron.I guess not re the BB connecting.
I have the Venus GX. But If I make settings in the EG4 hub, will those settings override the Victron devices?