This is a shunt in a caseAre you grounding the negative class T? Hard to tell for sure but looks like a bare ground and has me confused.
View attachment 168778
The 6000W was at mid day. When it blew it was at around 500W (according to my emporia energy app).6000W won't blow one fuse.
Those battery terminals are far apart, unlike some other brands we've seen pictures of.
How long does precharge take? If too long and you rotated switch too soon, it would be defeated.
You read my mind. Was just searching for something appropriate. Would this work?I'd start eliminating some variables. Disconnect the charge controller first.
Replace the fuses with some breakers to keep the cost down.
I usually count to three and watch the display kick in on the inverters.
Good plan.Not sure what voltage that would be. DC/DC converter putting out 5V, what minimum input required?
Put a volt meter on it next time, see what voltage it has risen to by the time you usually switch on.
"Usually"?
How often does this need to be done?
I’m in Alberta - Canada, which is fairly dry all year round. In terms of specific humidity, no idea. Placement is in the back of my garage, so no a lot of movement, moisture etc.What is your humidity? You need to have some proper insulation between the busbars and the wood (bolt and wood as well).
Hey, they were both blue sea fuses (little fuse). I would like them to be a bad batch, but I doubt it.What make are your fuses and fuse holders, are they from a reputable reseller. They could just be bum fuses. And yes I would always go for a circuit breaker over a fuse.
By the way do I see you passing current through the wooden front of your battery box via a bolt? If so this is a big No-No because the wood will compress over time and your connection will become loose and then hot and then burn. You must have none compressible connections as battleborn have found out with their batteries.
I don't like to see "f 50 Hz" for something described as a DC breaker.
Find manufacturer's spec sheet, see if it is rated for DC, and what AIC in that
How do you adapt for the terminal lug size? I have 4/0 currentlyHere is a proper DC breaker of the same style - https://www.amazon.com/gp/aw/d/B09P4SHSML?psc=1&ref=ppx_pop_mob_b_asin_title
And here is an inexpensive din rail alternative - https://www.amazon.com/gp/aw/d/B0B1WBT8YK?psc=1&ref=ppx_pop_mob_b_asin_title
I am using both types.
If your lugs will not fit on the Dihool, you will have to cut the lugs off and crimp on the smaller size. I think it comes with them.How do you adapt for the terminal lug size? I have 4/0 currently
Thanks will do.Spark, from a loose connection.
Use a wire brush lightly on the threads.