timselectric
If I can do it, you can do it.
- Joined
- Feb 5, 2022
- Messages
- 19,796
CorrectThe Neutral coming from the Grid is called the grounded conductor in the NEC (it is grounded from the transformer to a grounding electrode)
Incorrect.and is the main part of the grounding system for the main service panel.
It is part of the return path for ground faults. When the source is the grid.
But the beginning of the premises grounding system is created at the premises N/G bond.
The reason that they are bonded at the first means of disconnect. Is to give the grounding system a low impedance path back to the source.This is the reason that neutrals and grounds are bonded in the main panel.