Another thing I hope we can all agree on is that it’s better to run the EGC back now from the array to the SCC or inverter location (even if there turns out to be some combination of system types that may or may not require bonding to the EGC for the 120/240 system). Because that would be future proofed against changing system types or misunderstanding how to do
Code allows you to install an auxiliary ground rod. But it's not recommended.
But if an auxiliary ground rod is installed, it must be connected to the grounding system.
You are mixing up GEC and EGC all over the place. I suggest you spend more time understanding 250 before you try to understand why you are incorrect.
Also, read the FPN in 690.47.
I think there is more to this story. The original question was about grounding his system that has a ground mount. So looking at the 2020 NEC, Article 250, Part VIII. Direct Current Systems applies. In 250.160 General it states that DC systems shall comply with part VIII and other sections of Article 250 not specifically intended for AC systems. So #1, whatever is intended only for an AC system does not apply to the ground mounted DC array. #2, 250.162 DC Circuits and Systems to be grounded. DC circuits and systems shall be grounded as provided for in 259.162(A) and (B). 250.164 Point of Connection for DC Systems is divided between off premises or on premises sources. An off premises source shall not be made at any point on the premises wiring. Is a ground mounted array considered off premises? I’m not questioning anyone’s expertise, experience or knowledge. I thought I would share this information. If I had my inspector hat on, I would say a ground mounted array is off premises and roof mounted would be on premises. Just my thoughts.