Ordinarily odd cell voltages are a sense wire connection problem. Those are not.I'm looking for advice on my setup. I have 8s 24v system with 3.2v Catl cells, and i just received my Xenes 150a bms (copy of the Daly). Finally managed to connect via urt cable, but the numbers are strange. It says two of the cells are at 5.0 volts, and the rest are ok. Could someone take a look at the photos and tell me what to do. I have not charged them yet, top balanced them until all were 3.27v. I have Powland hybrid inverter which i'm going to connect battery to.
Thanks for the advise.
Edit: well those pics suck, i'll take better ones if needed.
Contact the vendor and get a new BMS (unless you hooked two wires up to a 5v power supply).
FYI, 3.27v is not a top balance. The word top has meaning in this context.
I also recommend changing balance voltage to 3.4v, not 3.2v (after you top balance).