Disable battery usage (charge&discharge) - EASUN Isolar SM II-5kVA

Timebis

New Member
Joined
Apr 4, 2020
Messages
1
On my solar system, i use
- 1 EASUN Isolar SM II-5kVA (see attached documentation)
- 1 DIY LifePO4 90Ah 17s battery
- 1 raspberry to create a dataLogger and to add security&control layers.

I would like in some case the load supplied by the {grid + solar} while having the battery connected but not used at all.
I would like to enter this mode : 1702811548953.png
I only manage to enter in it when my battery is disconnected..

Does sb have a idea how can we manage that with the parameters available ? And if it is possible ?
 

Attachments

  • ISolar SM II-5KVA_manual.pdf
    3.1 MB · Views: 7
  • HS_MS_MSX_RS232_Protocol_20140822_after_current_upgrade.pdf
    184.6 KB · Views: 5
Setting 1 is where you set it to do what you want. The problem is that inverter doesn't have a SUB mode which is required for a true hybrid mode like your wanting. On my tp6048 I have it set to SUB which is solar first and if solar isn't enough use utility(grid) and the grids down use the battery.

Without the SUB mode I don't think it can do what you want.
 