To clarify, that is not OP's schematic, that is a quick and dirty example (attempt) at drawing one version of what OP may want (which is yet to be completely defined) but the two main parameters are < 24V and a goal of 15kW AC output. The schematic is not what OP is building necessarily, simply an example of something in the same ballpark.
Four batteries delivering 1000A to two inverters?
That's exactly what I was hoping for.
Not necessarily, that is just one example of the concept OP is pursuing (multiple inverters + multiple battery packs). The number of inverters and packs may differ, but I believe this is the general design they are shooting for. It was meant to illustrate a concept, and play with the numbers, not be a final design.
Please see the other thread for context.
I can do that with a 250A busbar (without it breaking a sweat)
Is that safe/advisable/leaving enough margin? Particularly in the case of battery packs going offline due to BMS disconnection or other issues?
Just have to get rid of that silly chokepoint that is a shunt, otherwise I need a 500A busbar. Use 2 or 4 shunts and sum the values?
That is certainly an option. the schematic is not OP's design, just one quick and dirty example. I don't know much about large systems with parallel packs, Shunts could be per pack or per system, Victron makes shunts upto 2000 or 3000A I think, so either option is feasible. I used 1000A shunt assuming 1000A busbar so it wasn't a limitation in that scenario. Personally I think I would want Bank level SOC, but like I said in the previous post, multi-pack designs are much outside my experience or comfort zone designing.
24V why? At 48V it would be half the current and 1/4 the power loss in wiring.
Read the other thread. Short answer is treat it as a design constraint, OP has been advised multiple times 48v makes more sense for such a high power requirement, but has his reasons not to go that route (and is aware that it is not ideal to stick to 24v).
You could use two busbars and put two 500A shunts between them.
Is the shunt just for your monitoring, or does it need to feed into any of the equipment to track state of charge?
Shunt is for the example only, not one of OP's stated design requirements.
How was one 1000A shunt supposed to connect to the two busbars in original drawing? Obviously not with a single 4/0 cable! Maybe two in parallel?
If it were me (and since I drew the example, I suppose it is me), I would use copper bar to connect the shunt to the busbars directly (similar to
this or
this. I suppose 2 x 4/0 could work but its not what I envisioned), alternatively something like the
Victron Lynx system (which was the inspiration for that part of my design, an which I'm sure is not cheap--but a 24v 15kw system is not going to be cheap) would accomplish the same goal and be safer and simpler.
4/0 and "designed for 375A" suggests 750A is the continuous load, since one cable each to two inverters.
Correct, 750A is a rough (and slightly conservative) estimation of OP's max power requirement (15kW)
15,000W / 0.85 inverter efficiency / 24V = 735A
It is also roughly the current each remaining battery pack would have to handle if 1/2 of them go off line.
But again, all these details are mine not OP's, his design requirements were 15kW on the loads side, and 24v system voltage, multiple parallel battery packs. The diagram is not meant to be a blueprint but more of a rough concept sketch of one maybe-possible solution
(see previous thread).[/QUOTE]