Yay - finally have a shipping label created by CC today for my 6000xp ordered back on 10/30. ?
I'm especially glad since my current EG4 3000 EHV unit acquired a problem somehow - I can only charge it from (or even have it connected to) the grid if I turn off the inverter. It worked perfectly for a few months, and then one day the inverter turned off and it had a fault light with an over voltage error code. I eventually discovered that if I disconnected the grid input, the inverter works perfectly and also charges from solar, and if I turn off the inverter I can connect the grid input and charge it from AC when needed, but I can no longer have it connected to the grid and have the inverter on at the same time. So strange. I also found that the AC input terminals have 120 volts from line to ground - but only when the inverter is on. I connected an LED smart bulb connected to the AC input terminals to see if there was any actual power behind the voltage, and it was enough to light up the bulb. Argh. I have no idea why it would be fine for months and then suddenly have this issue.
After I replace it with the 6000xp I'll try and work with SS on the 3000 unit, but I did open up the unit to put the N-G bonding screw in place to see if that would make a difference (it didn't). I hope I didn't void the warranty by doing so.