I run 58 Kwh on one BMS. Not hard to do. One Watchmon Core with 4 K9's.Effectively, 7-15kwh batteries using all one singular BMS? That doesn’t sound fun at all
Yes, that was my reasoning as well. A cell fails, the other packs dumping massive amounts of current into the pack, the fuses not able to handle it/arcing, cells (or even just one) venting, and the arcing fuse igniting the vent gasses. If the current was high enough, probably none of the fuses on the different packs would be able to quench the arcs (which is why a high AIC is required for these). I do wonder how that high of a current could develop even with a single cell shorted.
The Batrium would see a low/high cell voltage according to the parameters set for cell low/high critical event. Also, there is a temp sensor for each group of 4 cells and if an overtemp occurs (according to parameter set), it also is a critical event.I also wonder what the BMS was doing...
The Batrium would trip the shunt trip breaker.
This however doesn't prevent current from flowing between each 16S set of cells. In my bank, each 16S set has a Class T 175A fuse. A solid 1/4" x 1" copper busbar runs down each side of the battery bank box. One side of the box is positive, the other is negative. All of the 16S positives have a solid busbar from the last cell to the Class T fuse and a solid busbar from the Class T fuse to the main copper busbar running down the side.Shown here during assembly with protective wooden covers over the terminals to help prevent accidental shorts.
On the opposite end, each 16S negative is connected with a short 2/0 cable, sorry, no photo, didn't think it was important.
One thing about my bank is it is contained inside a Hoffman industrial electrical box that is about 1/8" thick. I purposely used this cabinet for fire protection reasons. It would have to get pretty hot to burn thru it. That is why they are built heavy. I ensure often there are not any combustibles put around the box such as a cardboard box.
As for the OP's battery bank, yes, it should have had a Class T between each 16S set. Second, heavy construction of a cabinet in my mind is paramount. When in doubt, build it stout. Take my shelves for instance. Each one is double rectangular tubing of 1/8" wall with a center bracket welded in to prevent any twisting of the tubing. Each end has a heavy angle iron bracket welded to the rectangular tubing with a pair of 3/8" bolts thru the cabinet wall. These cells are heavy and any sag in a shelf will lead to failure down the road.