I tested the grounding of the AIMS 12v to 220v split phase inverter with a plug in receptacle tester. It shows that while in battery mode that the neutral is internally bonded to ground, therefore the neutral and ground are not bonded at the panel.
You just explained very well what happened at a place I worked at years ago…it was part retail in front of a diesel repair shop in the back with the most God awful electric system thst was 60 + years old and had been modified by the old timers working there a hundred times ..they had ground rods everywhere you looked , wore out wires run here and there…it was scarey to look at..Definitely not a good idea, on a rainy day.
I should add a disclaimer. lol
That's a N/G bond. Nothing fake about it.I bonded neutral and created a fake ground in a wiring box
What's fake is I can't bond it to the inverter ground, the bat neg terminal, the shell of the trailer etc. It's a local only ground, an alternate path to get back to the center tap of the transformer.That's a N/G bond. Nothing fake about it.
That's the beginning of a standard grounding system.
The only thing that needs to be isolated is the battery negative (and positive of course).What's fake is I can't bond it to the inverter ground, the bat neg terminal, the shell of the trailer etc. It's a local only ground, an alternate path to get back to the center tap of the transformer.
So, battery negative is internally connected to the inverter enclosure.The battery is isolated, not a starter battery. It's isolated by virtue of having two dedicated #0000 wires run for bat neg and pos to a breaker and a bus bar, and to the inverter. No trailer shell connection.
The best I got for "grounding" on this is an AC circuit specific AC ground and neutral tie, and probably staking the trailer shell and attaching the inverter ground to the shell. The shell can't be connected to neutral or bat neg. It'd be an electrostatic ground only.
The inverter documentation specifically calls out not binding neutral to bat neg or inverter ground, it has to float ?
I just don't like it, it's possible to get a shock by grabbing either bat terminal and AC neutral. Not that I would do that intentionally.
An inverter that ties neutral to ground internally, and has an isolation transformer would be safer. I have to be mindful of screw depth and stuff and metal to metal contact in lieu of a good inverter.
I bonded neutral and created a fake ground in a wiring box, it will act as a return path and outlets test ok.
I do feel these inverters carry a bit of danger. A misplaced screw touching a trailer shell and you have a hot skin.
I wonder if it is worth adding an isolation transformer on the output as is...
In that situation you will have to leave the AC output floating. I would at least use a GFCI.
RightI would use GFCI with L and N connected, ground left unconnected. Leviton works, the Eaton I tried did not.
Eaton won't work in some situations.Nothing wrong with Eaton.
Do you mean you bonded neutral to the ground pin of an outlet? If so, and if neutral can't be bonded to chassis because current will flow, it sounds like chassis of any device (e.g. corded drill) with 3-prong plug would be hot, a shock hazard.
Well, current would not flow to chassis if I connected neutral to chasis. Right now chassis is floating. Current would flow of I connected bat neg and neutral to chassis. Current may flow if I connect inv chassis to chassis, and neutral to chassis. Inv chassis does not seem to be bonded to bat neg terminal internally according to multimeter. There is some sort of decoupling cap specifically on inv ground pin.
I think the best thing to do is to invest in a good inverter in my case, and let the chassis float or be tied to earth.
That looks pretty good to me.hi @FilterGuy - Could you please review these connections? I
had asked in other groups but wanted to double/triple confirm. I have a Schneider XW pro 6.8k inverter with mini-pdp with connections to main, batteries and sub-panel. I have AC ground coming in from the main but no ground going to the sub-panel from the inverter. I have Ground connected between main and sub-panel(6 awg). The XW document says to connect from XW to sub-panel but in the diagrams that they have, it does not have a connection from the XW to sub-panel.
Also, do I need to ground the DC side?
DOC:
Diagram from Doc:
Another sheet from their documentation:
thank you
BTW: you could have a ground from the sub-panel or the ground from the main panel to the sub-panel, but don't do both (It would create a ground loop)hi @FilterGuy - Could you please review these connections? I
DOC:
Diagram from Doc:
thank you
Lets start with the easy part of the answer. You should definitely ground the rack and tie the ground points of the batteries to the Rack. Typically people will daisy chain all the battery ground points together and then one connection to the rack.Also, do I need to ground the DC side?
Great.That looks pretty good to me.
Are you planning on having loads that need more than the 6.8KW of the inverter when it is in passthrough? The reason I ask is that when I design for a main box separate from the critical load box, I don't typically load up the critical load box with more than what the inverter can drive..
If your loads are never going to exceed what the inverter can drive, then the max continuous current is 6800W/240=28.3A. With that current you could use a breaker sized at 28.3 x 1.25 = 35.41A. Round up to 40A for the breakers and 8AWG for the wires.
Ground points - Would that be from negative bus bar to the rack since they are all in parallel?Lets start with the easy part of the answer. You should definitely ground the rack and tie the ground points of the batteries to the Rack. Typically people will daisy chain all the battery ground points together and then one connection to the rack.
The more difficult part of the answer is whether the DC circuit itself should be grounded. Most people don't ground the circuit. However, this does not square with the part of the NEC code that says any circuit over 50V should be grounded (Either the negative side or positive side, the code does not specify). This quandary has always left me a bit uneasy..... particularly since I don't know what the equipment is expecting. Will the inverter or battery get upset with a grounded circuit? Does the inverter keep the DC circuit from floating significantly above earth ground? I used to recommend grounding the DC circuit because, in general, floating circuits are not a good thing ..... but now I am not as convinced. As I said, it seems like most people don't ground the DC circuit and the inspectors don't flag it.
No. I am talking about the metal case of the battery and the metal rack.Ground points - Would that be from negative bus bar to the rack since they are all in parallel?
So I think from there is a ground point on the door (the yellow wire at the bottom in this pic). So run it from there to the Inverter AC ground (maybe using 12 awg)?No. I am talking about the metal case of the battery and the metal rack.
I just went and looked at the LiFePower4 and realized they don't have ground points. (I would have bet they did). Since they don't have ground points, I would use star washers on the mounting points to make sure there is a good connection from the battery to the rack. That is not great, but better than nothing.
I don't know what server rack you have but there is likely to be a ground point on it somewhere. Tie that to the rest of the AC ground.
Verify continuity with a meter.So I connected the battery rack ground to the inverter ground. What would be a proper way to test this?