I recently purchased a cheap inverter to use as a backup power source for my gas furnace in the event of a power outage. (This is in the US).
The inverter is 1500W continuous (3000 watts peak), which is adequate for my needs. 12V DC input, 110V Ac/60 Hz output. It is supposed to be a pure sine wave inverter, although I have no means to verify that.
The product details can be seen here: https://www.aliexpress.us/item/2255...t_main.21.8d951802ybxCXB&gatewayAdapt=glo2usa
My question is about bonding ground to neutral. I will connect the furnace to the inverter output using an extension cord, as such it will be a “separately derived system” and the neutral needs to be bonded to the ground terminal for safety. Also, the furnace will not operate if it does not see ground (it is a high efficiency furnace and as I understand it they need to see ground, presumably to ensure the flame sensor operates properly).
The inverter, while it appears to work well, unfortunately comes with no documentation. The seller (manufacturer?) is Chinese and of not much help, possibly because of language difficulties. The only thing they can tell me is that both AC output terminals are live. I have verified by using a multimeter that both are live and floating, with no reference to ground. I will not be connecting any part of the inverter to my house AC system.
Measurements were as follows: NCV feature on the multimeter does not detect any live voltage, however the “Live” setting (single probe from the multimeter) indicates both terminals are live. 115V AC measured between the 2 terminals, about 49V AC measured between each terminal and metallic case (“ground”), but no shock if I touch the case. Voltage between ground terminal of the AC outlet and house system ground shows indeterminate (fluctuating 20-30V AC) voltage. The outlet ground terminal (socket) does not appear to be connected to anything, not even to the case. Voltage between the case and the ground terminal is about 5V AC.
However, if I use a Fluke multimeter on the LowZ setting, then I measure 0.6 volts AC between either of the 2 live terminals and the case, and 0V between either of the 2 live terminals and my house electrical system ground.
This leads me to believe that the voltage being measured between live and case in the non-LowZ mode is a phantom capacitive coupling, would that be right?
The website (listing) has the following info:
Both of the inverter outputs are live wires, and there is no grounding problem. Do not use any one as a ground wire. Connect the inverter to the load. Do not connect any air switch or leakage protection switch in the middle. Hard operation will not only fail to protect, but will damage the inverter.
I have connected a GFCI/RCD between the outlet and a test load and it seems to work fine, not sure why they say leakage protection (which I assume is a GFCI/RCD) will damage the inverter. Any thoughts?
But my main question is will it be safe to bond the one of the outputs (any one I suppose) to the case and designate that output as the neutral, and bond the case to the outlet ground socket. I assume this will not electrify the case (cause a shock) since there is no reference to earth but I am concerned that it might damage the inverter, especially since I am currently (unbonded) measuring about 49 V between either of the 2 live outputs and the case. I think I have read somewhere that the possibility of inverter damage exists, but not sure. The seller also said: Do not use any one (output terminal) as a ground wire
On the other hand, if it is just a ghost voltage then I think I should be safe to bond one of the output terminals to the case and designate that as neutral/ground.
Any recommendations on that would be very welcome. If there is anything I can check by opening up the inverter, please do suggest.
If anyone has a typical schematic for such an inverter I would really appreciate that too.
Thanks in advance.
The inverter is 1500W continuous (3000 watts peak), which is adequate for my needs. 12V DC input, 110V Ac/60 Hz output. It is supposed to be a pure sine wave inverter, although I have no means to verify that.
The product details can be seen here: https://www.aliexpress.us/item/2255...t_main.21.8d951802ybxCXB&gatewayAdapt=glo2usa
My question is about bonding ground to neutral. I will connect the furnace to the inverter output using an extension cord, as such it will be a “separately derived system” and the neutral needs to be bonded to the ground terminal for safety. Also, the furnace will not operate if it does not see ground (it is a high efficiency furnace and as I understand it they need to see ground, presumably to ensure the flame sensor operates properly).
The inverter, while it appears to work well, unfortunately comes with no documentation. The seller (manufacturer?) is Chinese and of not much help, possibly because of language difficulties. The only thing they can tell me is that both AC output terminals are live. I have verified by using a multimeter that both are live and floating, with no reference to ground. I will not be connecting any part of the inverter to my house AC system.
Measurements were as follows: NCV feature on the multimeter does not detect any live voltage, however the “Live” setting (single probe from the multimeter) indicates both terminals are live. 115V AC measured between the 2 terminals, about 49V AC measured between each terminal and metallic case (“ground”), but no shock if I touch the case. Voltage between ground terminal of the AC outlet and house system ground shows indeterminate (fluctuating 20-30V AC) voltage. The outlet ground terminal (socket) does not appear to be connected to anything, not even to the case. Voltage between the case and the ground terminal is about 5V AC.
However, if I use a Fluke multimeter on the LowZ setting, then I measure 0.6 volts AC between either of the 2 live terminals and the case, and 0V between either of the 2 live terminals and my house electrical system ground.
This leads me to believe that the voltage being measured between live and case in the non-LowZ mode is a phantom capacitive coupling, would that be right?
The website (listing) has the following info:
Both of the inverter outputs are live wires, and there is no grounding problem. Do not use any one as a ground wire. Connect the inverter to the load. Do not connect any air switch or leakage protection switch in the middle. Hard operation will not only fail to protect, but will damage the inverter.
I have connected a GFCI/RCD between the outlet and a test load and it seems to work fine, not sure why they say leakage protection (which I assume is a GFCI/RCD) will damage the inverter. Any thoughts?
But my main question is will it be safe to bond the one of the outputs (any one I suppose) to the case and designate that output as the neutral, and bond the case to the outlet ground socket. I assume this will not electrify the case (cause a shock) since there is no reference to earth but I am concerned that it might damage the inverter, especially since I am currently (unbonded) measuring about 49 V between either of the 2 live outputs and the case. I think I have read somewhere that the possibility of inverter damage exists, but not sure. The seller also said: Do not use any one (output terminal) as a ground wire
On the other hand, if it is just a ghost voltage then I think I should be safe to bond one of the output terminals to the case and designate that as neutral/ground.
Any recommendations on that would be very welcome. If there is anything I can check by opening up the inverter, please do suggest.
If anyone has a typical schematic for such an inverter I would really appreciate that too.
Thanks in advance.