So you pump in 20Ah per 9 months of balancing current from an extra charger, that works out as 74mAh per day? The Batrium wiki says 50-150mAh per day for cells "at the end of life", so I guess this is in the ballpark. The question then would be why the Batrium BMS needs help from an external charger and doesn't take care of this by itself. Their balancers seem to all be good for a lot more than 74mAh per day.
.15Ah is mentioned here:
Set Up The AutoLevel Bypass Configuration On The WatchMon
How to Set Up The AutoLevel Bypass Configuration On The WatchMon
wiki.batrium.com
EVE 280Ah cell datasheet indicates up to 1% self-discharge per month.
That's 2.8Ah/month or 2.8/30 = 93mAh/day
So brand new EVE cells may be at end of life by the 50-150mAh/day number.
What if a 10,000Ah cell lost .15ah per day. Cell would hold its charge for 183 years. End of life?
I love my Batrium, but they can be complete dolts. Their claim without any context is meaningless. Anything they say goes into the "I need to confirm this somewhere else" bucket.
To this day, their directions for interfacing with a Victron system is still not fixed. I notified them two years ago. They fail to tell you a key setting, and they instruct you to do something completely stupid.