The LVX is a split-phase unit with the ability to charge batteries and feed the grid at the same time. THe LVX6548 is the newest upgrade to the LV 6048 & LVX6048.
Grounding is NOT an issue if you use the panel ground. There is a separation between the neutral and the ground on secondary panels, so depending on If you are at the main grid-tied panel or a secondary panel, this would be your only grounding concern. Use the grounding side if this is a secondary panel, as you are not to bond the neutral and ground on a secondary panel by NEC.
Grounding is NOT an issue if you use the panel ground. There is a separation between the neutral and the ground on secondary panels, so depending on If you are at the main grid-tied panel or a secondary panel, this would be your only grounding concern. Use the grounding side if this is a secondary panel, as you are not to bond the neutral and ground on a secondary panel by NEC.