Hi GLC,I run battleborn batteries. This information is supplied from battleborn.
User Settings
Update for Case SUP21927 - "New Inquiry Battleborn Batteries - 2022-01-06 14:50:02"
Good evening,
I listed the EPever settings below:
Battery Charging Setting User 12 volt/ User24 volt 4-batteries Also use 200 AH setting for 4 batteries at 24 volt Over voltage disconnect voltage 14.7V / 29.4 charging limit voltage 14.6V/ 29.2 over voltage reconnect voltage 14.6V/ 29.2 Equalize charging voltage Off or 14.4V/ Off or 28.4 Boost charging voltage 14.4V / 28.4 Float charging voltage 13.6V/ 27.2 Boost reconnect charging voltage 13.3V/ 26.6 Low voltage reconnect voltage 12.0V/ 24 Under volt. warning volt 11.5v or Off/ 23 Low volt. disconnect volt. 11.0v/ 22 Discharging limit voltage 10.5 or Off/ 21 or off Equalize duration (min) Off/ off Boost Duration (min.) 30 minutes per 100Ah battery bank 30/ 120
Setting up the EPEVER Solar Charge Controller
The Epever MPPT solar charge controller has become a popular option for many customer applications. Find out how to set it up here!
battlebornbatteries.com
I'm looking at these settings on battle born website and seeing some difference below. Could you verify? Thanks!
1. Low Voltage Reconnect you wrote 12v/14v but on the website it shows 10v
2. Equalize Duration (min) you wrote off but on the website it shows 0
3. Boost Duration (min) you wrote 30/120 but on the website it shows 180min (for 12 v??)