Here is a diagram of the system we had set up and showed in our Youtube video.
I still want to see all grounds bonded together with copper wire. Not two separate ground networks.
The output is not separately derived. When on-grid, L1 and L2 reach through to your inverters, loads, etc. so requires ground back to service entrance, and I think neutral back to service entrance as well.
I say this design will actively drive the two ground rods to different voltages when on grid and loaded unevenly between the two phases.
Earthworms frantically wriggle to the surface.