Safety hazard w/ Growatt 5000ES (European version) when connected to American grid

That does not address the fact that the input is designed for one leg to be at or near ground potential.

Basic Engineering 101
 
That does not address the fact that the input is designed for one leg to be at or near ground potential.

Basic Engineering 101
But it’s not. There’s no specific electrical requirement for that to be the case. The grounding can happily be established at the auto transformer
 
The inverter INPUT is designed for one leg to be at or near ground potential.

Using a Euro inverter on a split phase grid puts 125 vac on the input designed for at or near ground potential

The autotransformer only deals with the OUTPUT of the inverter

The ONLY safe way to use a EURO inverter on a split phase grid would to use a full isolation transformer on the input as well as using the full isolation transformer on the output which is wired 230 volts in and 120/240 volts out

AND the neutral path must be continuous.........I.E. split phase neutral from utility connected to the INPUT full isolation transformer OUTPUT (neutral) terminal and then connected to output full isolation transformer neutral terminal

But then again do what you want, I legally cannot suggest do what you are trying to do

I do not need the liability
 
The inverter INPUT is designed for one leg to be at or near ground potential.

No it’s not. The invertor does not care where the L1 and L2 are referenced . ( in fact many euro mains are not ground neutral ground referenced at all. ) in this scenario. Break any neutral ground connection as it shouldn’t be there.
Using a Euro inverter on a split phase grid puts 125 vac on the input designed for at or near ground potential
No the input is 240VAC ie the potential difference
The autotransformer only deals with the OUTPUT of the inverter

Correct this shoujd only be used in invert mode only.
The ONLY safe way to use a EURO inverter on a split phase grid would to use a full isolation transformer on the input as well as using the full isolation transformer on the output which is wired 230 volts in and 120/240 volts out

Sorry there’s no justification electrically for that.
AND the neutral path must be continuous.........I.E. split phase neutral from utility connected to the INPUT full isolation transformer OUTPUT (neutral) terminal and then connected to output full isolation transformer neutral terminal

But then again do what you want, I legally cannot suggest do what you are trying to do

I do not need the liability
If you use a 240 VAC single phase invertor do not connect it to ground , The output is floating.

To get split phase then use an auto transformer and in invert or grid tied mode connect the centre tap ( ie neutral ) to the system ground

The key is to regard the invertor as a “ component “ and not a generator output.

The problem only occurs if you inadvertently ground the invertor and reference it’s output to ground. This is wrong if the split phase output is then also grounded.

It’s simple if you are going down this route regard the “ auto transformer “ as the invertor output and ground as normal.
 
Last edited:
That does not address the fact that the input is designed for one leg to be at or near ground potential.

Basic Engineering 101
In a euro invertor , no that assumption is false as several countries floating L1 and L2 rather like the US split phase. In euro land you never assume the neutral is at ground potential ( Italy is TT for example )
In many cases homes are fed with three phase directly so again all TT basis

( Norway is for example fed as per US split phase approach, two live conductors to get 230 )

Americans tend to sssume Europe is electrically like the U.K. this is absolutely not the case.

As I says the provision of auto bonding neutral ground relays is controversial in Europe, Many regulators feel this should be done externally.
 
Last edited:
This is how I connect my components.

We use USA system (120v/240v split phase) in my country but there is no ground bar on the utility meter (so there is no bonding neutral-ground) on any house in my country, most Plugs are 2 legs on all houses.
 

Attachments

  • 5000ES(US) With  breakers autoTransformer.png
    5000ES(US) With breakers autoTransformer.png
    86.2 KB · Views: 15
Last edited:
Auto transformer will establish a midpoint between two wires 240V apart.

If the 240V single-phase inverter has two connections "L" and "N", does the "N" comply with creepage and clearance requirements to be operated 120V above ground? The inverter should be designed and tested for that.

It does appear that with proper switching an auto transformer can let a 240V isolated inverter interact with the 120/240V split-phase utility grid and also supply split phase when grid is disconnected. Victron has a product for that.

Some of the schematics I've seen, when connected to grid, if a fault occurs between line and chassis the breakers will not clear it and chassis remains hot.

You have to determine not only that the system will function properly when everything is good, but also that it will remain safe when any faults occur.

This is how I connect my components.

We use USA system (120v/240v split phase) in my country but there is no ground bar on the utility meter (so there is no bonding neutral-ground) on any house in my country, most Plugs are 2 legs on all houses.

In your drawing: https://diysolarforum.com/attachments/5000es-us-with-breakers-autotransformer-png.118315/

You are missing a ground connection back to the utility meter.

If a fault develops between incoming L1 or L2 to inverter chassis, your entire ground network is now at 120V.
Some current will flow through the earth due to your ground rod off the breaker panel, but not enough to trip "AC breaker" at utility meter.
Touching your equipment and anything (e.g. water pipe) with other ground connection will result in a shock.
 
Auto transformer will establish a midpoint between two wires 240V apart.

If the 240V single-phase inverter has two connections "L" and "N", does the "N" comply with creepage and clearance requirements to be operated 120V above ground? The inverter should be designed and tested for that.

It does appear that with proper switching an auto transformer can let a 240V isolated inverter interact with the 120/240V split-phase utility grid and also supply split phase when grid is disconnected. Victron has a product for that.

Some of the schematics I've seen, when connected to grid, if a fault occurs between line and chassis the breakers will not clear it and chassis remains hot.

You have to determine not only that the system will function properly when everything is good, but also that it will remain safe when any faults occur.



In your drawing: https://diysolarforum.com/attachments/5000es-us-with-breakers-autotransformer-png.118315/

You are missing a ground connection back to the utility meter.

If a fault develops between incoming L1 or L2 to inverter chassis, your entire ground network is now at 120V.
Some current will flow through the earth due to your ground rod off the breaker panel, but not enough to trip "AC breaker" at utility meter.
Touching your equipment and anything (e.g. water pipe) with other ground connection will result in a shock.
I have 2 supervisors with a contactor that check L1 L2 and N faults.

I cant connect the ground on the meter because others house don't have it, if a fault on N on my street occur all N of the street are going to try to use my ground. Like i say i don't know why in my country there is no ground on the meter, but it work like that since we have electricity here...

1667057842434.png
 
Last edited:
I have 2 supervisors with a contactor that check L1 L2 and N faults.

Residual current detector, disconnects if ground leakage occurs?
That may do what is needed in your situation.

For people in the U.S. using these European models, neutral at the meter is grounded and they don't have that RCD (GFIC) breaker, so it is a problem.

Maybe if U.S. customers fed the inverter through a 2-pole GFIC it would solve that particular issue.
They may yet experience some voltage offset of their grounded center tap, so some current flowing through the earth (earthworms franticly wriggle to the surface.) You could see the same if a neighbor also uses an auto transformer.
 
This is how I connect my components.

We use USA system (120v/240v split phase) in my country but there is no ground bar on the utility meter (so there is no bonding neutral-ground) on any house in my country, most Plugs are 2 legs on all houses.
This cannot be correct as you as creating the same problem as the US system. and you have a complete floating neutral
 
Residual current detector, disconnects if ground leakage occurs?
That may do what is needed in your situation.
No it disconnects if the lve feed and neutral return currents differ
For people in the U.S. using these European models, neutral at the meter is grounded and they don't have that RCD (GFIC) breaker, so it is a problem.

No it’s not.
Maybe if U.S. customers fed the inverter through a 2-pole GFIC it would solve that particular issue.
They may yet experience some voltage offset of their grounded center tap, so some current flowing through the earth (earthworms franticly wriggle to the surface.) You could see the same if a neighbor also uses an auto transformer.
No need just leave the invertor float establish neutral bonding at the Auto
 
Auto transformer will establish a midpoint between two wires 240V apart.

If the 240V single-phase inverter has two connections "L" and "N", does the "N" comply with creepage and clearance requirements to be operated 120V above ground? The inverter should be designed and tested for that.

Yes it does it must. EU regs do not assume neutral is any difference to live.
It does appear that with proper switching an auto transformer can let a 240V isolated inverter interact with the 120/240V split-phase utility grid and also supply split phase when grid is disconnected. Victron has a product for that.
There is no issue as long as you do not neutral bond at the invertor
Some of the schematics I've seen, when connected to grid, if a fault occurs between line and chassis the breakers will not clear it and chassis remains hot.

You have to determine not only that the system will function properly when everything is good, but also that it will remain safe when any faults occur.
No. Chassis is never connected to neutral. It’s connected to ground.
 
This cannot be correct as you as creating the same problem as the US system. and you have a complete floating neutral
All my country is a big floating neutral and it work, not sure why the engineer here do this, i know the correct way is ground all the houses on the meter and bound it to neutral but what i can do? i have to put working my system and always use good protection and pray to god (lol) when working with the inverter.
 
Fundementslky here is the misunderstanding of the role of ground and its relationship to neutral
 
All my country is a big floating neutral and it work, not sure why the engineer here do this, i know the correct way is ground all the houses on the meter and bound it to neutral but what i can do? i have to put working my system and always use good protection and pray to god (lol) when working with the inverter.
Yes sorry , i agree as I said many European countries have fully floating neutrals
 
No it disconnects if the lve feed and neutral return currents differ

Correct, it actually measures difference between line and neutral. What I meant was, if ground leakage occurs (like a person getting a shock between line and ground), that results in a few milliamps difference between line and neutral so GFCI detects that and disconnects.

No it’s not.

No need just leave the invertor float establish neutral bonding at the Auto

If people in the US use a European 240V inverter and an auto transformer, several issues occur.
If their inverter and auto-transformer were just used as a "generator" through a transfer switch, no problem. But feeding grid through the inverter, there are several issues. The Victron design appears correct to me.

No. Chassis is never connected to neutral. It’s connected to ground.

Chassis of inverter is bonded to ground.
Chassis of utility meter and disconnect switch is boded to ground.

At least in the U.S., neutral of utility is bonded to ground at about the first disconnect.

In the drawing Pendrak provided, neutral was bonded to ground at the breaker panel. Neutral from breaker panel wired to neutral of the transformers and loads. Ground wired to breaker panel, autotransformer, inverter, loads.

The so-called "neutral" of the inverter did not wire to ground because it was really "line". (in the case of a split-phase inverter, its neutral would bond to ground somewhere. In my case that is at utility entrance.

Pendrak's drawing showed a neutral at the utility meter, not connected to anything. (Don't know for sure but think it is a center tap of utility transformer, but not grounded in his country he said?) For anyone in the U.S. using that schematic, I've got problems with it, starting with "ground" not connected between utility meter and inverter. Correct that and I'll probably find another problem.

What I said was,
"You have to determine not only that the system will function properly when everything is good, but also that it will remain safe when any faults occur."
Do you disagree?
 
While an auto transformer is a bit of a hack true. It’s perfectly safe and usable
It is a terrible hack and completely stupid and potentially extraordinarily dangerous on so many fronts. Yes of course you'll produce your split phase 120 volts and your American light bulb will light up and you can put your cheesy grin on YouTube and exclaim hey it works but it is a fucking stupid thing to do.
 
Correct, it actually measures difference between line and neutral. What I meant was, if ground leakage occurs (like a person getting a shock between line and ground), that results in a few milliamps difference between line and neutral so GFCI detects that and disconnects.
It doesn’t have to be a ground fault current
If people in the US use a European 240V inverter and an auto transformer, several issues occur.
If their inverter and auto-transformer were just used as a "generator" through a transfer switch, no problem. But feeding grid through the inverter, there are several issues. The Victron design appears correct to me.
The key using a auto transformer is to regard the inverter feeding it as a “ component “. Hence there should be NO earth neutral bond established there in the 240 vac inverter because what you are doing is bonding a live to earth.
Victron do the same thing
Chassis of inverter is bonded to ground.
Chassis of utility meter and disconnect switch is boded to ground.
The bonding of the chassis to ground is irrelevant , it’s the bonding of neutral to ground at the inverter is wrong


At least in the U.S., neutral of utility is bonded to ground at about the first disconnect.
Yes that’s not the issue here
In the drawing Pendrak provided, neutral was bonded to ground at the breaker panel. Neutral from breaker panel wired to neutral of the transformers and loads. Ground wired to breaker panel, autotransformer, inverter, loads.
That drawing is fine , as there should be no bonding in the inverter between neutral and ground.
The key point is Neutral PE cannot bond at the inverter and the centre tapnof the suto transformer
There can only be one neutral PE bond per system.
The so-called "neutral" of the inverter did not wire to ground because it was really "line". (in the case of a split-phase inverter, its neutral would bond to ground somewhere. In my case that is at utility entrance.
Yes in the 240vac European inverter in a US split phase system , the key point is the neutral cannot be bonded as it’s actually L2
Pendrak's drawing showed a neutral at the utility meter, not connected to anything. (Don't know for sure but think it is a center tap of utility transformer, but not grounded in his country he said?) For anyone in the U.S. using that schematic, I've got problems with it, starting with "ground" not connected between utility meter and inverter. Correct that and I'll probably find another problem.
In his country , as I mentioned neutral is floating. Many European countries have floating neutrals, ie in effect it can be regarded as L2. It’s no difference from US split phase

That diagram is fine for the US , as long as the inverter does not bond L2 ( ie a floating neutral ) to earth.



What I said was

"You have to determine not only that the system will function properly when everything is good, but also that it will remain safe when any faults occur."
Do you disagree?
Yes but clearly people here seem to think neutral is the same as earth. Neutral is a “ live wire “
 
It is a terrible hack and completely stupid and potentially extraordinarily dangerous on so many fronts. Yes of course you'll produce your split phase 120 volts and your American light bulb will light up and you can put your cheesy grin on YouTube and exclaim hey it works but it is a fucking stupid thing to do.
There is nothing unsafe. The issue here is people assuming European neutral is not a live wire and therefore can be automatically bonded to earth

A European 240 invertor produces a waveform identical to US split phase 240 , ie L1 and L2 , assuming frequency is the same. , since L2 on US split phase IS NOT neutral or earth bonded , then why would you bond the European L2 to earth. This output is essentially a split phase. This is the key confusion here and the error people are making

The auto transformer regenerates a neutral from the then 240 “ split phase “ from the 240 invertor

Then you can now ground reference that neutral from the Auto transformer , by bonding , essentially recreating the US split phase . By bonding it to earth

This is no different to a US split phase invertor , just regard the 240 inverter and auto transformer as one complete unit.

Hence the takeaway is simple , if you are using a European inverter to generate US240vac , dont assume you have a live and neutral output , you don’t , you have two live outputs , do not bond a live output to earth,

( an RCD in the output will add protection from inadvertent shock paths but isn’t needed per say.)
 
Last edited:
I am not qualified or smart enough to justify all of this hack work, I just read what far more intelligent and knowledgeable people than us have written on here in the past and take their advice to heart.
But the more that people try to argue this is a perfectly fine situation the more I realize it actually is not and I wonder what some people's motives are.
Ac voltage is a weird and wonderful thing that can really hurt us if we disrespect it, just like DC voltage.
I feel very fortunate to be able to learn from far clever people than me on here.
I worked for Kodak in main labs on three phase 400 volt machines with highly conductive liquids and I respected the living daylights out of that shit because one wrong move and I was very dead.
 