Well f&ck me running. Is this my fault? I had everything torqued properly and it was my understanding i could wire thhn directly into my battery terminal blocks. Southwire said 1/0 cable but 1 gauge was all i could fit in the block and the manual says to just follow local code for wire sizing.
Conext MPPT 100/600 to my xwpro. Noticed a burning smell this morning after pushing only about 3.4kw through for two hours or so. systems been up and running for a month with no problems; not even a whiff of anything wrong till this morning. No events on the mppt log. Around 6kw/90a had been my max output during peak hours.
Godd@mmit. I assume this isn't fixable.
Anything I should know to help avoid this in the future? My ego's bruised thinking i did something wrong but be brutal anyway please, i need to make sure this doesn't happen again.
TIA.
Conext MPPT 100/600 to my xwpro. Noticed a burning smell this morning after pushing only about 3.4kw through for two hours or so. systems been up and running for a month with no problems; not even a whiff of anything wrong till this morning. No events on the mppt log. Around 6kw/90a had been my max output during peak hours.
Godd@mmit. I assume this isn't fixable.
Anything I should know to help avoid this in the future? My ego's bruised thinking i did something wrong but be brutal anyway please, i need to make sure this doesn't happen again.
TIA.