Think the rule of thumb is 5x to7x running amps for inductive loads. My pump running after first 2 seconds is 5.8a or 1400w like clockwork. Starting inrush is always just over 37a so approx 9000 watts.
My neighbor bought a harbor freight ac/dc meter for $99 that measures ac inrush. It was not far off from my fluke, about .25 amp.
Would love to have someone prove that these inverters in split phase can start a deep well pump. Understand that my 9kw surge is under total capacity of 13kw but surge power overall is no joke.
I am having the same issue with my pair of 6500's in split phase but mine is above ground - a 2 hp well pump.
It simply will not start. When it tries, all the voltage drops on both legs enough to dim the lights and cause my ups to beep (like a power hit on grid).... then bounces back to normal. Interestingly, no faults on the inverters at all.
Previously, I had a single es5000 running the pump. It worked fine, except when the pump started - and it did start and run properly. The inverter beeped, said 100% load for a split second, then continued on it's merry way. I definitely need to get a meter to check inrush current, but I have 30 amp breakers and they are not tripping.
The SPECS of my pump are as follows: HP: 2.0 / F.L.A 8.3 / S.F 1.4 / S.F.A 12 / Volts: 230 / HZ 60.
So I read this as:
The Full Load Amperage (FLA) - the amount of current the motor is designed to draw at the rated horsepower) = 8.3.
The Service Factor Amps (SFA) - the overload capacity of the motor. Ultimately, SFA indicates how much your motor can run without sustaining damage = 12
The S.F. is a multiplier applied on top of FLA (ok, to be technical it is applied to horsepower.... I don't make a distinction but some in this forum will) = 1.4 - I don't know how this affects the power calculations.
Unfortunately, it does not state what the inrush / starting current will be.
Assuming that it is 7x (worst case as you state above) of the FLA (8.3A) - that would equate to be 58.1 amps. - how many watts is that????
Is that under the 13KW surge rated? I expect that is the reason the pump is not starting.
Thoughts?