Im new too but some things you might consider.
To charge batteries the panels have to produce more than the load. The extra goes to batteries.
The sooner your panels hit charging voltage in low light the better. This might also help you choose between 12or 24V setup.
Battery charge rate and discharge rates need to allow the amperage you plan on utilizing both from panels and to inverter. This include the combined starting surge.
Usage will definitely vary depending on environmental conditions. I have a new 100w fridge that draws 10w per hour on 300+ hours of kilometer monitoring. 10whr right? It climbed up to 80whr on initial startup.
I've conducted an audit for 2 months daily. I know when these run and for how long in 4 hour increments. 700 wh is the most they use during off peak hours. I manipulated them to do that to a degree. I noticed the cycling pattern and simply unplugged them until I got most of the load to be after 10 a.m. at that point the sun has been hitting them for almost 2 hours. The entire wh use per day was 2310 max in summer. A freezer is fine this time of the year unplugged for up to 3 days thawing and at least 1.5 days in the middle of summer. A 300ah battery will have more than enough to provide during a day of low solar. A 600 watt array is sufficient in a perfect world but bare minimum. This will be 1500w total. Over half minimum required for a load of 210 watts with all 3 appliances running so it's a light load that isn't continuous. So hopefully this will cover even a mostly cloudy day. The system has its own panel. Three 15 amp breakers per appliance. Right next to those outlets 2 inches away is a grid outlet. I don't expect it to develop power in extreme cloud conditions but I do expect it to be self sufficient in up to 60 percent. If I don't see that happening more panels it is until I can run it with a candle ?