High AIC fuses are only required on the battery(feeder) circuits.Ok, so how do people feel about the need for T-class fuses "beyond" the main system fuse(s). Assume batteries and battery banks are all fused correctly (enough AIC, correct size to protect wires). Is there any actual NEED for T-class level AIC on branches? In theory if a 50A fuse blows and there's a 5000A arc the main T-class is ALSO going to blow and it has sufficient AIC. I think the only concern is if you used a fuse with such a low AIC that it could form an arc that would NOT kick the main fuse(s).
The branch circuits can get away with lesser fuses.
The branch fuses can break on over-current, but are not guaranteed to break a dead short.
In a dead short on a branch the BMSs will likely cascade trip if the branch fuse sustains an arc.
If any of the BMSs fail closed then the high AIC feeder fuses are the last line of defense.