@wholybee wrote
Understood, one 3 way switch. I like it and will make that change.My only change would be that there is no manual disconnect, and the Emergency switch allows paralleling of the batteries. So, I would change the emergency switch to a "1-2-off" type between the manual bypass and the lynx distribution.
- LFP Bypass
- Off
- SLA Emergency
- No both. Don't want to parallel the batteries (not compliant with ABYC.
That would be something!With [the components shown] , ie. REC BMS , you have very fine control over charging limits , especially as you can
What would be nice would to add the ability in the Cerbo to instruct the REC to reconnect the battery , this would even allow remote ( via victron VRM ) ability to reengage charge sources etc.
- run DVCC on the Cerbo Gx
- Control all Mppt and alternator charge sources , allowing central control.