Interesting..... I did not see anything in the documentation that mentions arc fault sensing in the tail unit..... Maybe I missed it. Can you point me to any documentation about it? ThanksThere's a tail module on every panel, thus why I have 32 tail units to go with my 32 panels. The arc fault circuitry is built into every tail module, not the head unit, which is used to help monitor the performance of the system. I haven't researched the details, but I highly doubt the tail units switch open with a pro-active signal, since they have a heartbeat signal, and will open if they don't receive it. The cost was $950 for all pieces for me, landed in the US. (They're selling at wholesale prices to even us DIYers.) Don't confuse what I bought with the pic just above ... pretty sure that's a string level detector ...
Interesting..... I did not see anything in the documentation that mentions arc fault sensing in the tail unit..... Maybe I missed it. Can you point me to any documentation about it? ThanksThere's a tail module on every panel, thus why I have 32 tail units to go with my 32 panels. The arc fault circuitry is built into every tail module, not the head unit, which is used to help monitor the performance of the system. I haven't researched the details, but I highly doubt the tail units switch open with a pro-active signal, since they have a heartbeat signal, and will open if they don't receive it. The cost was $950 for all pieces for me, landed in the US. (They're selling at wholesale prices to even us DIYers.) Don't confuse what I bought with the pic just above ... pretty sure that's a string level detector ...
I attached a doc in the post you responded to ... note the arrow from their serial Arc Fault detector into the Tail Unit on slide 2 ...There's a tail module on every panel, thus why I have 32 tail units to go with my 32 panels. The arc fault circuitry is built into every tail module, not the head unit, which is used to help monitor the performance of the system. I haven't researched the details, but I highly doubt the tail units switch open with a pro-active signal, since they have a heartbeat signal, and will open if they don't receive it. The cost was $950 for all pieces for me, landed in the US. (They're selling at wholesale prices to even us DIYers.) Don't confuse what I bought with the pic just above ... pretty sure that's a string level detector ...
Hi @jesse_c I'm very curious how's your Fonrich arc detection integration with Tigo ended (if already finished)?Right, the part that I bought is meant to be integrated into an existing system. I already have a PVRSS system, and wanted to add arc detection and shutdown to it.
I'll admit I haven't done the installation yet. I have two inverters, one the arc fault appears to be working okay, the other it is not really working at all, with the 'self test' failing every day sometimes multiple times. unfortunately even after digging into the application code and finding the password to turn off internal arc fault detection, it is not permanent... turned itself back on the next day. So... i will likely need to open the sealed side of the inverter to bypass the art detection CT and then add the fonrich system as originally planned. Other house projects have taken precedence so far though. I'll take another look at it in the new year I think, as the rest of my energy monitoring system is more complete now.Hi @jesse_c I'm very curious how's your Fonrich arc detection integration with Tigo ended (if already finished)?
I have similar situation (inverter w/o afci and Tigo optimizers) and also looking to integrate stand alone arc fault detection.
What inverter do you have that detects arc-fault?I'll admit I haven't done the installation yet. I have two inverters, one the arc fault appears to be working okay, the other it is not really working at all, with the 'self test' failing every day sometimes multiple times. unfortunately even after digging into the application code and finding the password to turn off internal arc fault detection, it is not permanent... turned itself back on the next day. So... i will likely need to open the sealed side of the inverter to bypass the art detection CT and then add the fonrich system as originally planned. Other house projects have taken precedence so far though. I'll take another look at it in the new year I think, as the rest of my energy monitoring system is more complete now.
The built in arc detection won't trigger the RSD so it wouldn't extinguish a parallel arc fire, which was the original reason for getting the fonrich in the first place, so it is still high on my list of things to tackle.
Looked into this option (AFD triggers RSD) as a stand-alone AFCI solution and the only challenge with properly satisfying NEC is the discrepancy in clearing times. RSD code allows 30s for PV voltage to get to 80V, while the required AFCI clearing time is a function of arcing power, with max of 2 seconds (https://www.nrel.gov/docs/fy14osti/60660.pdf, pg 7). If you look into SunSpec rapid shutdown requirements, (pg 15) the transmitter is supposed to respond within 2s, but there is an additional 26s allowance for de-energizing and capacitor bleed off.My less-old Sunny Boy 10000TL-US and newer Sunny TriPower have arc-fault detection.
TriPower also has part of the RSD function: discharge of input caps when AC removed. May be part of a firmware update I received but haven't installed yet (I requested in order to have Rule-21). But no keep-alive so I've bought that separately (Tigo, who also makes the RSD boxes).
I would also like to trigger RSD in event of arc-fault, haven't figured out yet if there is a status output which could do that.
If I get a Sensata arc-fault detector working that could trip RSD.
Would the arc bleed down any capacitor within that time on the pv side ( now disconnected ), that'd be a function of the whole system and inverters.Looked into this option (AFD triggers RSD) as a stand-alone AFCI solution and the only challenge with properly satisfying NEC is the discrepancy in clearing times. RSD code allows 30s for PV voltage to get to 80V, while the required AFCI clearing time is a function of arcing power, with max of 2 seconds (https://www.nrel.gov/docs/fy14osti/60660.pdf, pg 7). If you look into SunSpec rapid shutdown requirements, (pg 15) the transmitter is supposed to respond within 2s, but there is an additional 26s allowance for de-energizing and capacitor bleed off.
I have been studying the NEC requirements for wiring solar panels and one of the requirements is arc-fault protection if the PV array is at 80V or more.
However, when I search for PV arc-fault protection product.... I find no stand-alone products.
I have not found a stand alone product.... Does anyone know of one?
- Some SSRs have it built in.
- Most grid-tie inverters have it built in.
- Some Solar optimizers have it built in.
- Some combiners have it integrated.
- Some Rapid disconnect systems have it built in.