Now that I have my conex for the power shack, things are falling into place. The next step will be to run underground cable from the conex to the cabin. The cabin is out in the country and completely off-grid. No code. No inspections.
I’ve got a bunch of 2” schedule 80 PVC and a fair amount of 2” rigid metal conduit. I’ll have a dedicated trench at 12” deep (no frost line) and run the schedule 80 as conduit with the part under the road in the rigid metal conduit.
I’m thinking I’ll run split phase AC to the cabin from some victron product/transformer in the power house. I’ll use copper. It’s about 75’.
I’ve got a couple of questions.
1. If I’m running split phase on an underground feeder line (3 conductors and one ground wire), I think I perform all my wire size calculations at 120 volt. Giving me 8awg. Does this sound right? There is no “there and back” as in DC, correct?
2. Is it a big mistake not to run 240 to the cabin with a transformer at the cabin? I am trying to avoid electrical hum in the small cabin. The 8 awg copper looks like it’s about $3/foot. Not terrible.
3. I’m thinking of a single grounding rod at the conex. The cabin will be a sub panel and grounded back to the conex ground. Am I on the right track?
4. Do I also ground the array to this ground rod?
I’m pretty new to most of this and any general thoughts also welcome.
Thanks I’m advance.
I’ve got a bunch of 2” schedule 80 PVC and a fair amount of 2” rigid metal conduit. I’ll have a dedicated trench at 12” deep (no frost line) and run the schedule 80 as conduit with the part under the road in the rigid metal conduit.
I’m thinking I’ll run split phase AC to the cabin from some victron product/transformer in the power house. I’ll use copper. It’s about 75’.
I’ve got a couple of questions.
1. If I’m running split phase on an underground feeder line (3 conductors and one ground wire), I think I perform all my wire size calculations at 120 volt. Giving me 8awg. Does this sound right? There is no “there and back” as in DC, correct?
2. Is it a big mistake not to run 240 to the cabin with a transformer at the cabin? I am trying to avoid electrical hum in the small cabin. The 8 awg copper looks like it’s about $3/foot. Not terrible.
3. I’m thinking of a single grounding rod at the conex. The cabin will be a sub panel and grounded back to the conex ground. Am I on the right track?
4. Do I also ground the array to this ground rod?
I’m pretty new to most of this and any general thoughts also welcome.