@rmaddy - quick question regarding your comment about needing a bigger than 40A inverter with the four 350W panels. What if I connect the four panels in 2S2P fashion? Would the 40A inverter then be OK? Thanks again.
SCC output amperage is not affected by PV panel configuration, input voltage, or input current. SCC takes in PV watts (volts x amps) at any voltage higher than battery, and switches an inductor to produce battery voltage at higher current. Similar to what a transformer does, but for DC.
PV_volts x PV_amps / battery_volts = battery_amps, which are delivered by SCC.
If you wire PV panels 2s2p and orient one "2s" South East and the other "2s" South West, about a 90 degree angle between them, area presented to sun will be about 0.7 as much, so peak current will be about 0.7x as much, and power harvested will be more flat and last longer through the day. Could be a better fit to your loads.
Also, I suppose if I upgrade to a 60A charge controller, I should upgrade its circuit breaker from 50AM to 70A, right? Or 80A?
When using fuses or thermal-magnetic breakers (or thermal breakers), it is recommended to size them 1.25x larger than continuous current.
Some magnetic-hydraulic breakers say 1.0x is sufficient.
The headroom is to prevent nuisance trips, which can happen due to hot day and heat from wire and connection affecting the element.
Consider lowest battery voltage when calculating battery current.
(For inverters, besides those factors, I also suggest an additional 1.12x factor because 60 Hz ripple causes additional heating.)
4000W / 24V / 85% efficient x 1.12 x 1.25 = 275A minimum fuse
So I would rather have larger than 250A fuse (and wire ampacity) unless you won't actually draw 4000W for more than a few minutes.
2/0 is OK for 300A if individual wires in free air (not bundle) and rated 90 degree C.
In this case I used 24V not 20V because that's around lowest voltage for LiFePO4. For lead-acid I would have used 20V.
8000W surge not considered because it is brief.