Is that one inverter, one MPPT input, fed from two separate combiner boxes with breakers?
The vendor may say to do that, but I would say do NOT. I do not believe polarized breakers (which can only interrupt current in one direction without arcing and burning up) can protect against backfeed into a damaged PV string from the other PV strings.
If each combiner box feeds a separate MPPT input, that is a step in the right direction.
Is it possible to gang all breakers in the box by slipping a wire through a hole in the handle of each one? If so, that would resolve my concern.
Or, put an anti-backfeed diode in series with each string. Then two boxes into one MPPT would be OK.
Or, get a combiner box with a touch-safe fuse holder for each PV string, and a single breaker as disconnect. That would be good with up to two combiner boxes wired to a single MPPT input even if the breaker is polarized.