Is it the Main panel or Subpanel? Need more info.
Also keep in mind when sizing the subpanel amps, it really need to be less than the main panel breaker. Because when the battery goes to 20%(no output) and no solar, All the subpanel amps (loads) will pass through the main breaker.
Newest manual https://eg4electronics.com/backend/wp-content/uploads/2023/04/EG4-18KPV-12LV-Manual.pdf
If the LOAD wiring and subpanel bus support it, though, do I really need a subpanel breaker smaller than 200a? I get that it could trip the main 70a breaker if I draw more than 70a, but having a sub panel breaker at 70a would trip too. I guess one is more annoying than the other but it's not a safety thing, no?Also keep in mind when sizing the subpanel amps, it really need to be less than the main panel breaker. Because when the battery goes to 20%(no output) and no solar, All the subpanel amps (loads) will pass through the main breaker.
Newest manual https://eg4electronics.com/backend/wp-content/uploads/2023/04/EG4-18KPV-12LV-Manual.pdf
Just wire it like you would an appliance. On the bus. On the opposite end.of the bus as the main 200amp breaker.The breaker in the main panel (where this is to be hooked up) has a main disconnect breaker labeled "200".
I have a 125 amp subpanel breaker. I was referring to total load of amps.If the LOAD wiring and subpanel bus support it, though, do I really need a subpanel breaker smaller than 200a? I get that it could trip the main 70a breaker if I draw more than 70a, but having a sub panel breaker at 70a would trip too. I guess one is more annoying than the other but it's not a safety thing, no?
Please clarify: you have a 200A main breaker on the load center and you are going to have the 18k supply the load center? Are you planning to do this by having the utility power go into the Grid side of the 18k and the Load side of the 18k goes to the 200A main breaker on the load center? Or are you trying to back-feed the load center through a breaker installed in the load center? No utility power, only solar? Or other configuration?The breaker in the main panel (where this is to be hooked up) has a main disconnect breaker labeled "200".
Please clarify: you have a 200A main breaker on the load center and you are going to have the 18k supply the load center? Are you planning to do this by having the utility power go into the Grid side of the 18k and the Load side of the 18k goes to the 200A main breaker on the load center? Or are you trying to back-feed the load center through a breaker installed in the load center? No utility power, only solar? Or other configuration?
From the "Load" to a breaker on the load center.From the "Grid" on the 18k to a breaker on the load center.
From the "Load" to a breaker on the load center.
At least that is my current thinking unless that thinking is faulty.
If my thinking is correct, then I need to know what size breakers to put in the load center to attach these two items too.
From the "Load" to a breaker on the load center.
Are you referring to the critical load subpanel? If you are talking about coming out of the main panel and go through the 18Kpv back to the main panel you need to change to a different wiring diagram. Look at the feeder tap diagram in the manual.
I don’t think it can be done that way. Maybe someone else can chime in on this.Coming out of the main panel to the Grid input of the 18KPV and then back to the main panel from the Load output in the 18kpv to the main panel.
why are you hooking the grid side of the inverter to the main load at all? What you describe is a circular path... what is your overall set up in terms of solar, battery, generator, grid?Coming out of the main panel to the Grid input of the 18KPV and then back to the main panel from the Load output in the 18kpv to the main panel.
why are you hooking the grid side of the inverter to the main load at all? What you describe is a circular path... what is your overall set up in terms of solar, battery, generator, grid?
OK no problem just wasn't sure if I was missing something. But what are the components in your set up? Grid or grid-less, solar or no solar, battery or no battery? If grid, what Amperage is your service? Inverter covering all loads or critical loads? Etc. Would help us to know those
Yes that's the only breaker.Great, that helps a ton. Last question: do you have any breakers upstream from the 200A load box? Like is there a breaker outside on or next to the utility service, that when you flip it cuts all power to the load box? Or is the 200A breaker in the load box the only breaker between meter and you?
I believe you have only two choices given those parameters:
1) you can use a supply side tap which will require the utility turning off the power while you tap into the lines from the meter, see the supply side tap w whole home backup diagram in the manual.
2) You can install a 200A breaker between the meter and the load center which also requires utility to turn off power, and then use a feeder tap that comes off the leg running from the new 200A breaker to the load panel, see feeder tap w whole home backup diagram in manual.
You can't connect to the utility by backfeeding through a breaker in the main panel because that method maxes out at 70A which isn't enough for your whole home backup