Luxpower_Gilbert
Luxpert @Luxpower USA Team
The inverter is pretty fast to de-energized the gen port when i did my test.Yup, this makes sense for on-grid and I have no worries about it. I want to understand your guarantees for off-grid better.
You have to sized your system correctly. If your not planning to sells to the grid then I recommend more storage. If you use more power during the day then more pv.The worry is if you max out the 16kW AC coupled, and it's outputting at 100% to satisfy 4kW of loads and 12kW of AC charger. If the loads turn off then there is risk of overvoltage damage until the FreqWatt or relay can react quickly enough. Or the AC charger has surge charging capacity to compensate and sink the current.
Inverter max charge output is 250A. Like i said sized your system correctly.This also depends on the BMS capabilities on the connected battery, for instance the PowerPro defaults to 100A charge, 200A discharge on a single battery. Now given the PowerPro surge spec I think AC coupling in 10-12kW on a single battery should be safe since I would be surprised if F-W response is too slow. This also does not require me to know the LuxPro AC charger's surge rating, since the continuous rating is enough to satisfy this.