They have pills for that.You will never be perfectly balanced. You just don't want to be heavily unbalanced.
They have pills for that.You will never be perfectly balanced. You just don't want to be heavily unbalanced.
The idea that the ends of a single phase system are 180 degrees out of phase is wrong, but it is understandable. They aren't out of phase, therefore it is geometrically incorrect to describe it that way. But they are opposite in polarity, so they are "180 degrees different" like you might say night and day are "180 degrees" apart. Ya know?Oh well, once again I am forced to put you back on ignore.
I’m guessing you might be referring to an ungrounded system? Popular in the cities from the 30-60s, it was cheap to install but deadly AF as fault current didn’t have a good path to ground/source.To really confuse things, at one point there were two phase power systems and a few are still running. I used to have to mess with them on rare occasions at the papermill I worked at. I also ran into 40 cycle AC systems at a very old papermill, I have a couple of solenoid valves that are rated for 40 cycle kicking around the house.
No, he's talking about a true two-phase system, where the phases are 90 degrees apart. They came in three flavors, 3-wire, 4-wire, and 5-wire. They were quickly overtaken by 3 phase. The only two phase system still in operation is in Philadelphia.I’m guessing you might be referring to an ungrounded system? Popular in the cities from the 30-60s, it was cheap to install but deadly AF as fault current didn’t have a good path to ground/source.
Also you can operate a three phase system/motors with only two phases, it’s called open delta. It works but is a but def a unique system and is probably only grandfathered in.
Which was my point. I started off by explaining that the supply in was 1 phase (to the central tapped transformer). Anyone that understands the design of a generator head understands how phases are created through the use of magnetic poles and windings. As the rotor spins against the stator the magnetic flux induces a voltage that corresponds to the windings passing the North or South pole. Thus a sine wave. It rises from zero as the pole is directly against the windings and drops off as the rotor turns and than rise as it passes the opposite magnetic pole but in a 180 degree opposite direction. A 3 phase genrator head has 2 more sets of windings and poles that are built into the generator that creates their own set of outputs.The idea that the ends of a single phase system are 180 degrees out of phase is wrong, but it is understandable. They aren't out of phase, therefore it is geometrically incorrect to describe it that way. But they are opposite in polarity, so they are "180 degrees different" like you might say night and day are "180 degrees" apart. Ya know?
There can be a good argument made for the European single phase 230v setup (though 50hz is a poor choice).I’m still trying to wrap my head around the wire cost savings for split phase.
It looks like one more conductor for split phase.
When looking up voltage drop for a split phase run of about 100’, do I use the 240 volt difference between L1 and L2 or do I use the 120 volt measured between each line and neutral.
With single phase, I get that more volts means less amps for a given watts. But with split phase, more volts compared to what?
Thanks
I’m still trying to wrap my head around the wire cost savings for split phase.
It looks like one more conductor for split phase.
When looking up voltage drop for a split phase run of about 100’, do I use the 240 volt difference between L1 and L2 or do I use the 120 volt measured between each line and neutral.
With single phase, I get that more volts means less amps for a given watts. But with split phase, more volts compared to what?
Thanks
2400 | W load | |
120 | 240 | V supply |
20 | 10 | A drawn by motor (rewired for given voltage) |
0.6 | ohms wire | |
12 | 6 | V drop in wire |
10.0% | 2.5% | of supply voltage |
The problem that Tim has is he refuses to acknowledge the apparent 180 degree.
I say this not to confuse ananyone.
I think I follow. IR is internal resistance of the wire, right?
In terms of sizing wire for a split phase run of 100’, I need to size them for a 3% drop for 120 volt uses, right? And that will necessarily cover the lower amperage 240 volt loads.
I read some info indicating that smaller conductors could be used for split phase. But I think those savings don’t come into play if I have both 120 volt and 240 volt loads. Am I close?
No he is not correct. Absolutely not. Simply because I was not and never have argued that there is 2 phases. Or that the two traces you see on the O-scope are indicative of 2 phases. Read though every post I made about the subject and if you can find me stating that it is 2 phases I will immediately apologize and never post to this Forum again. I am about at that point anyway. I absolutely hate to be mis-characterized or misconstrued deliberately.Because he is absolutely correct.
The phases are not 180⁰ opposite each other... there is only a single 240V phase.
The split point gives 1/2 the phase to each line relative to neutral.
He is stuck on the fact that the phase is not two different opposing phases...
However...
Even with true 3 phase... ALL PHASES ARE GOING THE SAME DIRECTION.
In 3 phase, they are seperated each by 120⁰, but they are all going the same direction... how else could they be... I mean, 3 phase isn't three different generators, it is one generator with three poles...
They ALSO have a center tapped neutral by the way... that produces 120V as well...
Anybody thinking split phase has two phases needs to explain how 3 phase gets 120V to neutral... is that then six phases? No, of course not...
Oh, I highly doubt he is responding to ONLY you in all his responses.No he is not correct. Absolutely not. Simply because I was not and never have argued that there is 2 phases. Or that the two traces you see on the O-scope are indicative of 2 phases. Read though every post I made about the subject and if you can find me stating that it is 2 phases I will immediately apologize and never post to this Forum again. I am about at that point anyway. I absolutely hate to be mis-characterized or misconstrued deliberately.
Funny enough but 3 phase is similar to 3 generators.
Getting into all the ways that you can create different voltages from combinations of using those 3 phases is lengthy and and I must admit it has been a long time since I took training in motor, generator theory.
I am good at noting patterns. It is what helps in troubleshooting.Oh, I highly doubt he is responding to ONLY you in all his responses.
And I don't think you ever said two phases either.
CorrectOh, I highly doubt he is responding to ONLY you in all his responses.
And I don't think you ever said two phases either.
And I'm glad that all of that is almost gone.To really confuse things, at one point there were two phase power systems and a few are still running. I used to have to mess with them on rare occasions at the papermill I worked at. I also ran into 40 cycle AC systems at a very old papermill, I have a couple of solenoid valves that are rated for 40 cycle kicking around the house.
208/120 you get 120 for phase to phase voltages not phase to neutral. Just like a leg of 240 to neural is 120v just with some phaser math involved.Because he is absolutely correct.
The phases are not 180⁰ opposite each other... there is only a single 240V phase.
The split point gives 1/2 the phase to each line relative to neutral.
He is stuck on the fact that the phase is not two different opposing phases...
However...
Even with true 3 phase... ALL PHASES ARE GOING THE SAME DIRECTION.
In 3 phase, they are seperated each by 120⁰, but they are all going the same direction... how else could they be... I mean, 3 phase isn't three different generators, it is one generator with three poles...
They ALSO have a center tapped neutral by the way... that produces 120V as well...
Anybody thinking split phase has two phases needs to explain how 3 phase gets 120V to neutral... is that then six phases? No, of course not...
And I'm glad that all of that is almost gone.
Delta high leg is also being phased out. At least in my area.
Install one 3-phase transformer on a pole and string 200' of wire to it (then the drop to my house.)
No thanks, I said. I'll just install PV, a 3-phase inverter, and disconnect from PG&E.