Oh, I may have sent the wrong link, I'm gonna double check my physical inverter in case, though. I'm pretty sure I ordered the 12v.Yea, matching voltage of subsystems:
Schematic says 12V battery and inverter link says 24V.
Just the main fuse and the bms.So besides the BMS, what else would you say is bottlenecking my system?
Also, if you have reccomendations for BMSs I'm all ears.
I can step up to 4/0 if that helps. I'll get on the lookout for a Daly 4s as well. Thanks for the help!Just the main fuse and the bms.
You could go a bit larger on the main wire and inverter wire as well.
I'm not a fan of Daly but you should look for a Daly 4s smart bms rated for 500 amps.
I guess that all depends on the fuse. I kind of like spending money.If that unit can do 4500 watts for 20 seconds it can likely do 3000 watts long enough to blow your fuse.
300 amps is the limit for mrbf fuses and that high amp fuseblock is probably also limited to 300 amps.
There is something I not fully understand - do you have a 12V battery bank or 24V? The battery configuration is not stated (or I did not catch it) but it looks like they are connected parallel. However the inverter you linked is 24V - 110V.So besides the BMS, what else would you say is bottlenecking my system?
Also, if you have reccomendations for BMSs I'm all ears.